Just thinking and want your opinions. I have to quote on a job which is a new house on a very large plot. The supply is currently a TNS to a point approx 10m from the house and a switch fuse plus armour takes the supply to the curret house.

The owner wants to build a new house and take a feed from the current meter to the house. Run is 40m of cable. Assume cable will be burried SWA.
I am wondering if I should go with 2 core SWA and make the house TT or go with 3 core SWA and leave it as TNS.

Roughly and using 3% volt drop it looks like the SWA is going to be around 35mm assuming a 100A load so an extra core is quite expensive not to mention making the cable dificult to handle. Calcs very rough so dont shoot me down yet.

I am currently thinking to go the TT route. What you guys think?
 
Just thinking and want your opinions. I have to quote on a job which is a new house on a very large plot. The supply is currently a TNS to a point approx 10m from the house and a switch fuse plus armour takes the supply to the curret house.

The owner wants to build a new house and take a feed from the current meter to the house. Run is 40m of cable. Assume cable will be burried SWA.
I am wondering if I should go with 2 core SWA and make the house TT or go with 3 core SWA and leave it as TNS.

Roughly and using 3% volt drop it looks like the SWA is going to be around 35mm assuming a 100A load so an extra core is quite expensive not to mention making the cable dificult to handle. Calcs very rough so dont shoot me down yet.

I am currently thinking to go the TT route. What you guys think?

I am thinking it would be cheaper to get DNO to install a service head than pay for the SWA :D
 
New house.....new connection.;)

What type of supply does the current house on the plot have???? single phase 100A max I'm guessing and you want to run another new house off it aswell??? Like Stuey, contact DNO and ask for new connection.
 
sounds like a good option to me. easy to not see the wood for the trees. Will see what the DNO says if the job goes any further, any idea what they charge for a new connection, London area.
 

Reply to to go TT or not in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
190
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K
I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
798

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top