To RCD or not...?! | on ElectriciansForums
Discuss To RCD or not...?! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
L
londonlec
Hey Guys,
Kitchen socket outlets within living accomodation in a boarding school?
I am altering/adding to the existing circuit.
My guess is cables buried <50mm won't need RCD as its a supervised environment.
But I feel the sockets will need protection.
I cant even find the DB at the moment, so am thinking along the lines of SRCD's.
Any views would be much appreciated!
If the new additions you add have cables that are buried <50mm then those cables need to be RCD protected. Being in a supervised area does not mean you can omit an RCD on cables buried less than 50mm. RCD the circuit in my opinion
As I couldn't (easily) locate the DB, I am concerned an RCD trip will knock out a whole floor until maintenance can find the RCD/RCBO.
I would agree with Hawk81, not sure if its must do under the regs, but i do know that all general purpose RCD's do need RCD protection. 415.1.1 and other regs in that area will clarify the situation. But whether or not the cables need RCD protection or not Hawks post does make good sense and if nothing else err's on the side of caution. If i recall there was a recent post regarding a teacher stapling kids posters to the wall ad hoc using a handheld stapler, one of which pierced the neutral conductor. So the install maybe under supervision, but Miss doesn't give a ---- when her kids posters need to be put up.
Cheers...........Howard
Is the kitchen a ring on its own?
I am not sure at the moment, without getting my fuse finder out.
I 'suspect' it is part of a large ring covering a few rooms (with stud walls).
My new cable will be chased in behind tiles, so unless 'Miss' is using a Paslode, we should be ok ;)
It is only for cables that there is an exception for the requirement to provide RCD protection if the installation is under the control of a skilled or instructed person.
Socket-outlets for general use by ordinary persons, must be provided with RCD protection, unless their use is to be supervised by skilled or instructed persons.
Bottom line here is the fact that we're discussing whether or not to spend ÂŁ25ish on an RCD/RCBO, or can we find a way to wriggle out.
The socket outlets can be used for general purposes, by unskilled people, and we can't guarantee mechanical protection of the cable that supplies them.
Where's the wriggle in that?
Im a Kiwi living In NZ where i should be, I dont know much about your Regs but by god the world of the Electrician is rife with rules and bloody regulations and all the idiots out there that electricute themselves just make the job so much harder.
I spent 2 hours today trying to establish why the RCD's I installed would not hold in, still haven't resolved the problem, i hate the bloody things.
I'm not wriggling. I am trying to avoid a fault in one room knocking out 5+ dormatories, which is my eyes is more dangerous/inconvenient.
Reply to To RCD or not...?! in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...