Carried out an EICR in a domestic property today.
Client has recently purchased but not moved in, so place is empty. It's a detached bungalow, 2 beds, Gas-fired system boiler, detached garage.
There are 7 (yes 7) socket outlet circuits, all either B16A or B20A, each with no more than 6 outlets. R1 + R2 readings suggest spurs a-plenty, although the readings aren't outlandish. On the other hand, most of the IR readings come in sub 10 megohms, with two of the circuits having IR readings lower than 1 megohm L-E. There is only one lighting circuit, with 12 switches/points including the gas system boiler. Aside from a handful of C3 or FI codes (including the abovementioned IR readings) it is Satisfactory, yet I can't help feeling it wants rewiring, especially as it is empty for the time being.
Your thoughts?
Client has recently purchased but not moved in, so place is empty. It's a detached bungalow, 2 beds, Gas-fired system boiler, detached garage.
There are 7 (yes 7) socket outlet circuits, all either B16A or B20A, each with no more than 6 outlets. R1 + R2 readings suggest spurs a-plenty, although the readings aren't outlandish. On the other hand, most of the IR readings come in sub 10 megohms, with two of the circuits having IR readings lower than 1 megohm L-E. There is only one lighting circuit, with 12 switches/points including the gas system boiler. Aside from a handful of C3 or FI codes (including the abovementioned IR readings) it is Satisfactory, yet I can't help feeling it wants rewiring, especially as it is empty for the time being.
Your thoughts?