Danielwareham

What would you be looking for when deciding if a house requires a full rewire or just updating i.e new consumer unit, main earthing, changing of some wiring and new circuits? What tests would you carry out and visual aspects would you be looking for?

Thanks
 
eerrmmmmm... Allot of it's experience and how much the customer want to spend.

Have a look at the fusebox and the cables coming out. If they're not PVC T&E then probably a rewire (although we recently did a PIR on pub where the rubber cables had an IR of >200).

Check for bonding, have a look at some loop values on different circuits, IR tests.... Depends on how much time you want to throw at it
 
IR circuits. visual check in accessories for any sign of cable damage/overheating. if rubber insulated or aluminium cable, or if green goo seeping. rewire.
 
If all the IR readings were all too low with no logical explanation, the cable were in generally poor condition eg crumbling VIR, everything wired in some odd kind of cable (eg 0.75mm 2 core flex, esp if on the final ccts), odd circuit arrangements eg cpc used as 3rd core in 2 way lighting, sockets wired in some kind of 'spider final' or something, wiring run out of safe zones, or all of the above.

I'd try to avoid a full rewire if possible - doing unecessary rewires willy-nilly can give us a bad name.
 
Some of what I was thinking and more! Cheers for the advice. Think I'll see what I can from the CU i.e if it's rubber insulated or aluminium cable, do some IR tests and check bonding. Then I'll do some loop readings. I think that will give me a good idea!
 

Reply to To rewire or not rewire? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

  • Question
Pretty common for lights and sockets to get a Re-wire and the Eco7 circuits usually storage heaters /water heater to remain left as was. As for...
Replies
14
Views
2K
Definitely, although most likely within the accessories. I've often found that once accessories are disconnected the cabling IR is fine. Sometimes...
Replies
19
Views
2K
The MCBs are branded Noark.
    • Like
Replies
5
Views
263
Replies
1
Views
2K
Kyle myatt
K
  • Question
There's something odd about that appliance inlet. Doesn't seem to have a base. Looks more like the type that should be attached to a flex.
Replies
10
Views
758

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks