RCD tripped. narrowed down to SWA feeding hot tub. never seen SWA connected like this before. armour not earthed anywhere. was supposedly professionally installed. the pic shows a 30mA plug-in power breaker RCD, the type you'd fit to a lawn mower cable!

[ElectriciansForums.net] today's fault

disconnected both ends and IR tested SWA . L/E 0.04 Meg. N/E 0.23 Meg. 40m of SWA, partly buried. half way down had been repaired? with choc block and tape.

so , it's quote for new SWA, glands, ad. box, correct installation. what i'm not happy with is that it's fed from the garage sub-main which is in turn fed from the house RCD in a split board, so a fault will take out all in the house except lighting. now, i've not done any work on hot tubs, but my thinking is to feed the garage sub. from the non protected side of the house ( it's fed in SWA ) and then fit RCBO in the sub. to cover the garage socket ( just a fridge/freezer) and a 13A FCU to feed the SWA to the hot tub. anyone see a flaw in this? worked out the VD at 13A to be 9.5V using 40m of 2.5mm SWA.
 
He might have been working on new builds for a long time. Does'nt seem like it though.
Anyone who thinks we were ever using steel as a cable conductor in house wiring has to come under a great deal of suspicion. May be polite, may also be very inexperienced.

Basics:mickey:

I was thinking the same myself
 

Reply to today's fault in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2 3
Replies
43
Views
3K
  • Question
wouldn't surprise me if we adopt this sooner or later...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top