tools list | on ElectriciansForums
Discuss tools list in the Australia area at ElectriciansForums.net
LONDON (barnet)
hello guys i am doing a project at college and am looking for a hand
got a booklet and need to do a tools list for testing and comisioning this
1) PVC twin and earth cable supplying;
A ring final circuit with six single socket outlets.
Three lighting points, one lamp with one-way control and two lamps with two-way control on a ‘loop system’.
2) An attached garage installation which is RCD protected supplied by a steel wire armoured cable from the main installation providing;
A single socket outlet for use with portable garden tools.
A one lamp one-way lighting circuit.
3) Main Equipotential and Supplementary bonding.
4) A special location – a bathroom with an electric shower with a pull cord isolator, an extractor fan with a 3 pole isolator, a ‘globe lamp’ on a pull cord switch, and supplementary bonding to the hot and cold water supplies.
5) A mineral insulated cable circuit supplying a DOL controlling a ramp lift motor.
6) Suitable isolation and over current protection for all the above items.
i need to have all the tools and also tests meters specificly any help would be great thx
Approved voltage indicator
Proving unit (if no live source present)
Lockoff kit
Low resistance Ohm meter
Insulation resistance tester
Earth loop impedance tester
RCD tester
Full set of insulated screwdrivers
A long R2 wander lead
Tape measure to confirm zones in special location
BS7671/On-site guide/GN 3 to check measure values comply
Label printer
Reply to tools list in the Australia area at ElectriciansForums.net
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
For a new circuit or alteration the dead tests should be done first to ensure it is safe to energise.
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...