As the title says, I was called by a company that fix aeroplane parts, they have a machine that is used for testing generators, it's stopped working and I was asked to have a look. I've told them it's way out of my depth and I pretty much don't have a clue, but said I would stop by and get a look at the machine and see if I could find any information out. Had a look and seen that the invertor display panel had ST-CC is open, had a look at the manual and it seems it needs to be closed for to run, has anyone worked on these before, or know someone that could fix it, I'm in Edinburgh, cheers!
 
Your board will have terminals similar to this ...so finding ST and CC should be easy... Screenshot (2).png

If you do find it and resolve it then just enjoy the brownie points but I only advised you on this one due to its possible simplicity to resolve but normally I would agree with your early statement regarding your honesty and admitting to the customer that its not your field or out of your depth.. these sorts of problems can get very involved and complicated very quickly.
 
Last edited by a moderator:
Its a run prohibit command like a stop circuit so need to be N/C so the drive can run when told to, it is open circuit at the moment so prevents the drive working when it receives a run command, you need to find out why its not a complete loop and look into my suggestions above.
 
Yeah I understand safety circuits etc, just need to find where the circuit goes so I can see where it is open. I appreciate the help and will give it a go if I can find what the ST circuit entails, if I can't get this sorted then I will leave it at that!
 
Would you ever link out ST and CC to see if it fixes the fault, ie brings the power back on to the machine, obviously done in a controlled safe manner?
 
Last edited by a moderator:
Would you ever link out ST and CC to see if it fixes the fault, ie brings the power back on to the machine, obviously done in a controlled safe manner?
I would not advise you to ever unless you understand exactly what you are doing and the risks involved - even just to test a theory, I do it but I do have the knowledge to do so... the diagram you posted is more complex than the one I sourced and may differ' but you need to refer to the manual for that exact model, you only supplied the brand and range, it seems there are a few variants/generations of the tosvert-130.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Livingston
Business Name
CM Electrical

Thread Information

Title
Toshiba Tosvert-130 transistor inverter issue
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27
Unsolved
--

Advert

Thread statistics

Created
Hellmooth,
Last reply from
Hellmooth,
Replies
27
Views
4,374

Advert

Back
Top