anyone tell me where in BS7671 it says what touch voltage is allowed for which special location - looked in individual special locations but can't see any mention :confused:

cheers.
 
411.5.3 applies universally now, Ra x Ideltan <= 50V where 50V is the maximum touch voltage. Pre 17th Ed BRB that equation <= 25V applied to certain special locations, eg. Construction Sites and Agricultural & Horticultural Premises.
 
Last edited by a moderator:
The forthcoming new amendment on medical locations sees the reintroduction of the 25 Volt touch voltage.

Do you know which locations it will apply to IQ ?

411.5.3 applies universally now, Ra x Ideltan <= 50V where 50V is the maximum touch voltage. Pre 17th Ed BRB that equation <= 25V applied to certain special locations, eg. Construction Sites and Agricultural & Horticultural Premises.
Hi Markie , yes quite a few references to 50V in brb and i was always under the impression that several special locations like the ones you mentioned were limited to 25V but i can't actually find it written in there:confused: Just can't remember if i have seen it written down or whether it has been people thinking of the 16th have been telling me.
 
Do you know which locations it will apply to IQ ?


Hi Markie , yes quite a few references to 50V in brb and i was always under the impression that several special locations like the ones you mentioned were limited to 25V but i can't actually find it written in there:confused: Just can't remember if i have seen it written down or whether it has been people thinking of the 16th have been telling me.

Yes, there is a new 'zone-type' system introduced on medical locations, the zones being called 'groups'.

The groups are numbered from 0-2 where 0 is the least 'intrusive' area eg. examination room/massage room and 2 where intercardiac procedures are performed and loss of supply can cause danger to life.

The 25 Volt touch voltage is introduced for groups 1 and 2 along with a new disconnection time for 230V Uo circuits of 0.3 Seconds (TN systems) and 0.05 Seconds (TT systems).

There are no other incidences of the 25 Volt touch voltage in BS7671:2008 or amendment 1
 
Yes, there is a new 'zone-type' system introduced on medical locations, the zones being called 'groups'.

The groups are numbered from 0-2 where 0 is the least 'intrusive' area eg. examination room/massage room and 2 where intercardiac procedures are performed and loss of supply can cause danger to life.

The 25 Volt touch voltage is introduced for groups 1 and 2 along with a new disconnection time for 230V Uo circuits of 0.3 Seconds (TN systems) and 0.05 Seconds (TT systems).

There are no other incidences of the 25 Volt touch voltage in BS7671:2008 or amendment 1

Bet there is a waiting list for your GP mate.......................;)
 
Looks as if BS7671 is adopting the German DIN VDE 0107 for hospital medical rooms. Which uses the same group designations as stated above. The German system is basically recognised as the international standard for electrical installations in hospital medical rooms/locations etc...

It'll be interesting how much of DIN VDE 0107 they actually incorporate?? There's quite a bit involved in the design side, let alone on the installation side of things...

This is the Standard i've worked too, on virtually all of my hospital projects, and is far superior to the present UK set-ups.
 
Looks as if BS7671 is adopting the German DIN VDE 0107 for hospital medical rooms. Which uses the same group designations as stated above. The German system is basically recognised as the international standard for electrical installations in hospital medical rooms/locations etc...

It'll be interesting how much of DIN VDE 0107 they actually incorporate?? There's quite a bit involved in the design side, let alone on the installation side of things...

This is the Standard i've worked too, on virtually all of my hospital projects, and is far superior to the present UK set-ups.

So gone are the days of ...............well stick either an IMD or more commonly an RCM on it and let the lights buzz then, I always found how deaf people were even with a 80Db audio alarm going on.

Yes did quite a lot of Phillip Holztmann work here in the 90's using the german standards, though I loved the copper work for the MRI unts. or when the cleaners come in with metal buckets.
 

Reply to touch voltages 50V and 25V in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
985
  • Question
That's brilliant Dave, thanks again. I had to raid my sons felt tips and pencils for any colours available! Apologies for the strange and...
2
Replies
24
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top