Hello all,
I could use some help here:
I was recently asked to do an EICR at a small warehouse/office unit.
The installation was, to put it mildly, less than satisfactory; with multiple C1 and C2 conditions. However, of greatest concern to me were the insulation resistance readings I was getting. I left the job, trying to explain the severity of the condition to the client, but still feel under the circumstances, he is unlikely to take any further action, despite his report been top to bottom in 'further investigation's.
Whereas I'm sure everybody on here has had this at some point (if not daily), it is the specifically the IR fails I am still scratching my head over.
2xsockets in floor boxes, 3xsockets in dado trunking, 3xlighting circuits, and 2xhand dryer spurs were all returning 0Mohms IR L-E, yet none of the associated breakers were tripping or had been problematic in any way. Breakers and board were old (maybe late 70s early 80s), no markings on breakers except obvious ratings, but I'm assuming wiring can't have been of same period unless floor boxes and dado trunking wre popular back then?? The decor and fittings were certainly more recent.
I was pleasently suprised to find a single A4 schedule of circuits reinforced with several layers of tipex and the board had a Ze and PFC reading written in it from 2002, but that was it for records.

Any thoughts???
 
As per usual, no actual figures.

I was under the impression that if a reading was <1MΩ the meter gave a reading in KΩ. I must be mistaken.

What I find annoying is the OP seems willing to condemn a system when he clearly hasn’t tested correctly.

Depends on the meter, on the 1720's we use if it's <1Mohm it shows 0.00 then you have to change the setting to continuity to measure the resistance

Loads of "sparks" are the same now though tony they just record whatever the meter tells them and move on, get the report out and condem an install which is still most likely in a serviceable condition
 
Depends on the meter, on the 1720's we use if it's


not me i passed

[ElectriciansForums.net] Tragic IR fail on EICR
 
Last edited:
1MΩ is a convenient figure dreamed up by the IET. It’s not the calculated value.

I’ll give you a scenario:
If you were to test a 50 year old 75HP 433V 3Ph motor, what would you accept for the supply cable minimum IR for L→L and L→E?
 
1MΩ is a convenient figure dreamed up by the IET. It’s not the calculated value.

I’ll give you a scenario:
If you were to test a 50 year old 75HP 433V 3Ph motor, what would you accept for the supply cable minimum IR for L→L and L→E?

is there a RCD on the circuit? :iamwithstupid:
 
1MΩ is a convenient figure dreamed up by the IET. It’s not the calculated value.

I’ll give you a scenario:
If you were to test a 50 year old 75HP 433V 3Ph motor, what would you accept for the supply cable minimum IR for L→L and L→E?

depends on the age of the cable but i would accept a low ir figure as long as it hasnt degraded a lot from last ir test. if last ir test a year ago was say 10Mohm and this year was 1Mohm i would fail it for example

i have no idea tony
 
Last edited:
It’s a motor in a plant, no E/L protection what so ever other than OCPD.

Keep out of this tel, let the youngsters have a go.
i was being facetious, tony. whoever heard of a RCD on a motor that size. :38:
 
This is from a genuine case, a plant with 250+ motors in a damp, dusty and cold environment. The motors ranged from ½ to 800HP.

The calculation is based on a maximum of 1/10000[SUP]th[/SUP] leakage of the circuit FLC.

2 x the Ph→Ph or Ph→E DC voltage is used for the tests.
For 433V you would use 1000V DC Ph→Ph or 500V Ph→E.

I said it was a rotten question, you need the FLC from the scant information I gave.

You need to calculate the motor FLC taking in to account efficiency and power factor. It’s an old motor so 92% efficiency could be a start 0.87 PF maybe?

But we’ll base this on 75HP 92% Ef 0.87 PF where 1 HP = 764W
There could be another way though.

Anyone care to carry it on?
 
Last edited by a moderator:
There are a couple of different calculations which have been used over the years.
For complete installations there was a calculation based on the number of circuits in the installation, I'll look it up when I get home later.
The other method I know is the one Tony posted above using 1/10000th FLC as the maximum leakage.
 
It is Saturday night so I’ll leave this until tomorrow evening.

As Dave said it’s an old method but in a large installation it’s invaluable.

I said earlier, 1MΩ was a global figure adopted by the IET for ease, it has no real foundation.
 

Reply to Tragic IR fail on EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

He only posted the one message then never came back.
Replies
2
Views
800

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top