dave440

Hi, part of my coursework is asking me to verify a series of test results.
The task is to explain any problems or deviations.

The results I have are related to a domestic ring circuit.
2.5mm cable.

the results I have are

Line1 : r/1, 0.27
r/n : r/n, 0.28
r/2, 0.45

My R1+R2 is 0.18

and my Zs is 0.34

I have not measured or calculated any of these values myself as they come from an exam question.

my task is to explain any problems with it, However I don't see anything wrong with them, am I missing something?

this is part of my homework and I'm getting a little desperate from some help.
 
Hi, part of my coursework is asking me to verify a series of test results.
The task is to explain any problems or deviations.

The results I have are related to a domestic ring circuit.
2.5mm cable.

the results I have are

Line1 : r/1, 0.27
r/n : r/n, 0.28
r/2, 0.45

My R1+R2 is 0.18

and my Zs is 0.34

I have not measured or calculated any of these values myself as they come from an exam question.

my task is to explain any problems with it, However I don't see anything wrong with them, am I missing something?

this is part of my homework and I'm getting a little desperate from some help.

2.5t+e with 1.5mm cpc?

might be be worth asking one of the mods for access to the trainee section as well mate.
 
Last edited:
Yes, will, however I need to leave my computer for about i hour, and I will return, I was hoping someone would be able to help me urgently, as I'm back at college tomorrow.
(everything at the last minute as usual!)
 
Hi, part of my coursework is asking me to verify a series of test results.
The task is to explain any problems or deviations.

The results I have are related to a domestic ring circuit.
2.5mm cable.

the results I have are

Line1 : r/1, 0.27
r/n : r/n, 0.28
r/2, 0.45

My R1+R2 is 0.18

and my Zs is 0.34

I have not measured or calculated any of these values myself as they come from an exam question.

my task is to explain any problems with it, However I don't see anything wrong with them, am I missing something?

this is part of my homework and I'm getting a little desperate from some help.

Have they told you what type of OCPD is being used?
 
The Ze I have been given is 0.17

Thats one of the things I'm suspecting also.
Although that's the Ze, there may be parallel paths from the bonding etc, which bring the Zs down below the expected value, hence the 0.14 ohm mentioned earlier.

Are there any more details for this question other than what you've already told us?
 
I would have bet your Ze at 0.16
As this is theoretical and not real, ZS-(R1+R2) = 0.16
As already said, on a real installation you would have parallel paths also.
There is also an allowance of 0.05 in your leads so it is all perfectly in order in my opinion as within 0.01
The 0.17 Ze may have been to throw you slightly with the 0.05 allowance
 
I would have bet your Ze at 0.16
As this is theoretical and not real, ZS-(R1+R2) = 0.16
As already said, on a real installation you would have parallel paths also.
There is also an allowance of 0.05 in your leads so it is all perfectly in order in my opinion as within 0.01
The 0.17 Ze may have been to throw you slightly with the 0.05 allowance

Thought the rule was to null your leads before any resistance testing???
 

Reply to Trainee Question for Inspection and testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I can't help wondering about earthing arrangements and how important aesthetics really are when attempting to make the best of a less than ideal...
2
Replies
21
Views
1K
nicebutdim
N
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top