Yes definatly. Even with the leads nulled, there is still a 0.05 margin.
Never heard that one, where do I find this info? or is it an unwritten rule?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Trainee Question for Inspection and testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yes definatly. Even with the leads nulled, there is still a 0.05 margin.
Yes definatly. Even with the leads nulled, there is still a 0.05 margin.
GN3 4.3 says about contact resistance and how it cannot be eliminated with two terminal testers. It however does not give the 0.05 value. It was when I did 2391 Course I was taught this, I have also spoke with NAPIT assessor on inspections who was aware of it.I remember rading in the GNÂŁ book about the slight diffferences and tollerances.
Unfortunately I d;t have this bok to hand right now. But would peopel be kind enough to confirm my ideas and opinions?
I wonder i the 0.05 allowance is the point of the question (to test my knowledge and catch me out).
The best answer I can think of, is that, the Measured Ze is 0.17, and the calculated Zs would usually be slightly higher.
So in this case, the Measured Zs is slightly lower due to possible parralel paths relating to maybe the water connection.
I remebered that the Ze is meaured without the parallel paths connected, but after energising, the parallel paths would be connected, and that might account for a slightly lower Zs reading.
Theres is no other information given to me, but (if eveyone else agrees), then I'm pretty sure I have found my answer.
(if anyone would like to scrutinise my opinion, I would be grateful.)
(Getting it wrong only means I learn more, so I have no problems with my answers being scruitinised).
Thank you so much!
I'm impressed that I'm finding the right answers!