Eh up!
A little scenario and a few questions related to it. It can be tackled by anyone at pretty much any level, so have a ponder and reply with your thoughts below. It's probably not the sort of thing you'll come across in your courses, but you'll certainly come across scenarios such as this in the real world...
The idea is to get you to cut through the usual BS about what you can and can't do, and get you looking at the statutory and non-statutory regs and guidance to either get a defiinitive answer, or at least form an informed opinion. I'll give you some hints on places to look to get their answers.
SCENARIO
You have been called to a domestic property - a fairly swanky-looking first floor apartment - where the owner reports that the bathroom extractor fan has stopped working. The details of the setup are as follows:
- The fan is powered from the lighting circuit, which is protected by a 10A BS EN 60898 Type B circuit breaker (as with many swanky apartments, there are LOTS of GU10 downlights!).
- There are no RCDs on any circuits in the property. The label on the consumer unit says it was installed in 2001.
- The fan is activated by a wall-mounted light switch (outside the bathroom) that turns on the bathroom lights, and has a run-on timer (so as well as a switched line, there is also a permanent line to the fan).
- There are no signs of an isolation switch for the fan.
- The fan is ceiling mounted.
- The height of the ceiling is 2m above floor level.
- The fan is adjacent to the shower (not over it), you estimate within about 400mm of the edge of the shower.
- The fan is not marked with a Class 2 label, and there is an Earth connection.
- The fan is rated IP44.
- The bathroom is interior, it does not have any windows or skylights.
Following safe isolation procedure and using appropriate dead tests, you confirm that there are no problems with the existing fixed wiring:
- Insulation resistance (L+N tied together to E): >299MΩ
- R1+R2: 0.60Ω, R1+Rn: 0.48Ω
- Switched line behaves as expected
As it is safe to do so, you also perform a measurement of the earth loop impedance at the fan: Zs = 0.80Ω.
You conclude that the old fan is faulty and needs replacement. Fortunately, a direct replacement (same model number) is available. As such, the client instructs you to replace the fan.
For the following questions, state:
- what is REQUIRED, or NOT REQUIRED, and if you can back it up with a reference (e.g. to BS 7671, Building Regs/Approved Document, other statutory regulation).
The Approved Documents are available from the Planning Portal: https://www.planningportal.co.uk/info/200135/approved_documents "Part P" relates to electrical safety in dwellings.
QUESTIONS
(1a) Does the work REQUIRE notification to Building Control?
(1b) Would you notify it?
(2a) In addition to the tests you have already done above, are there any other tests that are REQUIRED?
(2b) Would you do any other tests?
(3a) Does the work REQUIRE an Electrical Installation Certificate (EIC), a Minor Electrical Installation Works Certificate (MEIWC), an Electrical Installation Condition Report (EICR), something else, or none of the above?
(3b) What documentation, if any, would you issue?
(4a) Are there any additions or alterations to the existing circuit that are REQUIRED (in addition to the fan replacement itself)?
(4b) Are there any additions or alterations to the existing circuit that you would ADVISE the client need to be done?
(4c) For (4a) and (4b), do any of these REQUIRE notification to Building Control (and under what circumstances)?
(4d) If you advise the client of recommended additional work, what would you do if the client declined?
Finally, just to throw another fly in the ointment:
(5) You pick up the fan from the wholesaler. You have a quick read of the installation instructions. Under "electrical installation" the instructions state: "Means of double pole disconnection must be incorporated in the fixed wiring in accordance with the Wiring Regulations." You also notice that on the wiring diagram there is an item marked "3 amp fuse." Does this change any of your answers to any of the previous parts?
If you want to have a go at just part of it, or all of it, or ask questions... just fire away! I'll see how you get on, then I'll put up my thoughts, see what you think!
A little scenario and a few questions related to it. It can be tackled by anyone at pretty much any level, so have a ponder and reply with your thoughts below. It's probably not the sort of thing you'll come across in your courses, but you'll certainly come across scenarios such as this in the real world...
The idea is to get you to cut through the usual BS about what you can and can't do, and get you looking at the statutory and non-statutory regs and guidance to either get a defiinitive answer, or at least form an informed opinion. I'll give you some hints on places to look to get their answers.
SCENARIO
You have been called to a domestic property - a fairly swanky-looking first floor apartment - where the owner reports that the bathroom extractor fan has stopped working. The details of the setup are as follows:
- The fan is powered from the lighting circuit, which is protected by a 10A BS EN 60898 Type B circuit breaker (as with many swanky apartments, there are LOTS of GU10 downlights!).
- There are no RCDs on any circuits in the property. The label on the consumer unit says it was installed in 2001.
- The fan is activated by a wall-mounted light switch (outside the bathroom) that turns on the bathroom lights, and has a run-on timer (so as well as a switched line, there is also a permanent line to the fan).
- There are no signs of an isolation switch for the fan.
- The fan is ceiling mounted.
- The height of the ceiling is 2m above floor level.
- The fan is adjacent to the shower (not over it), you estimate within about 400mm of the edge of the shower.
- The fan is not marked with a Class 2 label, and there is an Earth connection.
- The fan is rated IP44.
- The bathroom is interior, it does not have any windows or skylights.
Following safe isolation procedure and using appropriate dead tests, you confirm that there are no problems with the existing fixed wiring:
- Insulation resistance (L+N tied together to E): >299MΩ
- R1+R2: 0.60Ω, R1+Rn: 0.48Ω
- Switched line behaves as expected
As it is safe to do so, you also perform a measurement of the earth loop impedance at the fan: Zs = 0.80Ω.
You conclude that the old fan is faulty and needs replacement. Fortunately, a direct replacement (same model number) is available. As such, the client instructs you to replace the fan.
For the following questions, state:
- what is REQUIRED, or NOT REQUIRED, and if you can back it up with a reference (e.g. to BS 7671, Building Regs/Approved Document, other statutory regulation).
The Approved Documents are available from the Planning Portal: https://www.planningportal.co.uk/info/200135/approved_documents "Part P" relates to electrical safety in dwellings.
QUESTIONS
(1a) Does the work REQUIRE notification to Building Control?
(1b) Would you notify it?
(2a) In addition to the tests you have already done above, are there any other tests that are REQUIRED?
(2b) Would you do any other tests?
(3a) Does the work REQUIRE an Electrical Installation Certificate (EIC), a Minor Electrical Installation Works Certificate (MEIWC), an Electrical Installation Condition Report (EICR), something else, or none of the above?
(3b) What documentation, if any, would you issue?
(4a) Are there any additions or alterations to the existing circuit that are REQUIRED (in addition to the fan replacement itself)?
(4b) Are there any additions or alterations to the existing circuit that you would ADVISE the client need to be done?
(4c) For (4a) and (4b), do any of these REQUIRE notification to Building Control (and under what circumstances)?
(4d) If you advise the client of recommended additional work, what would you do if the client declined?
Finally, just to throw another fly in the ointment:
(5) You pick up the fan from the wholesaler. You have a quick read of the installation instructions. Under "electrical installation" the instructions state: "Means of double pole disconnection must be incorporated in the fixed wiring in accordance with the Wiring Regulations." You also notice that on the wiring diagram there is an item marked "3 amp fuse." Does this change any of your answers to any of the previous parts?
If you want to have a go at just part of it, or all of it, or ask questions... just fire away! I'll see how you get on, then I'll put up my thoughts, see what you think!