M

mickys86

A transformer is rated at 10kw but is only delivering 9.8kw. Copper losses are 0.33kw and iron losses are 0.2kw. Calculate the efficiency of the transformer
A 88.6%
B 98%
C 90.4%
D 99%

I make the answer 91.33%

What am I missing??
 
Hmmmm the answer is actually c. Apparently. According to the Swindon massive site [ElectriciansForums.net] Transformer hypothetical question
 
According to my Hughes Electrical book,

eff=output power/(output power+losses) = 9.8/(9.8+0.53) = 94.87%

or more accurately...

eff= (input power-losses)/input power = (10-0.53)/10 = 94.7%

so I don't know.

Where's Tony?
 
According to my Hughes Electrical book,

eff=output power/(output power+losses) = 9.8/(9.8+0.53) = 94.87%

or more accurately...

eff= (input power-losses)/input power = (10-0.53)/10 = 94.7%

so I don't know.

Where's Tony?
The two equations are derived from first principles and are equivalent ways of calculating the efficiency of a transformer, neither is more accurate than the other.
The first answer is in error because the copper lossses are proportional to the load VI[SUP]2[/SUP], the copper loss at 9.8kW is therefore [0.33kW/(10/9.8)[SUP]2[/SUP]]= 0.317kW, the iron losses are approximately constant over the working load range, giving total losses at 9.8kW of 0.517kW.
So plugging these into equation 1:
eff = [9.8/(9.8+0.517)] x 100/1
eff = 95.0% (to 1DP)
The second answer is in error because the rated power 10kW is not the input power at 9.8kW.
From above the Input Power = Output Power + Total Losses
Input Power = 9.8kW + 0.517kW
Input Power = 10.317kW
Checking using equation 2
eff = (10.317-0.517)/10.317
eff= 95.0% (to 1DP) as was expected from equation 1
The above workings are based on the data provided in the OPs original question and as can be seen does not yield any of the multiple choice answers.
To achieve answer c) 90.4% the total losses would obviously need to be higher.
Total Losses = [(Output Power/eff)- output power]
Total Losses = [(9.8/0.904)-9.8]kW
Total Losses = 1.04kW
If we assume iron losses in the original question were correct at 0.2kW
Copper Losses = Total Losses-Iron Losses
Copper Losses = 1.04-0.2
Copper Losses = 0.84kW
Suggesting that the Copper Losses in the original question of 0.33kW might be a transcription error of the intended 0.83kW which would yield a rounded answer of c) 90.4% efficiency as proposed by Moses.
 
Last edited by a moderator:

Reply to Transformer hypothetical question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

Thanks little spark. Good point but the drivers I'm considering have a sync and communication between driver function. So (as long as it works)...
Replies
6
Views
589
  • Question
It was a one time ÂŁ19.99 fee. I'll be reaching out to them though to get that back. It was the only online extensive bank of questions that I...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top