I’ve seen a 110v control transformer reading 28v on the neatral to earth and 67 on the other leg. Why would this be?
 

Attachments

  • [ElectriciansForums.net] Transformer neutral reading 28v
    C174EEAD-3BAF-4E7C-BAFA-525095C3A089.png
    1.5 MB · Views: 549
The output is probably not earth-referenced, i.e. it is electrically separated / floating. The voltages to earth are not defined and the actual readings on the meter are not very meaningful, giving only a hint at the relative amounts of leakage / capacitance from the two lines. They will probably vary according to different instruments and a low-impedance meter might not show any reading. On a floating circuit what you do not want to see is zero on one leg and the full voltage on the other, as that might indicate a short to earth.
 
The output is probably not earth-referenced, i.e. it is electrically separated / floating. The voltages to earth are not defined and the actual readings on the meter are not very meaningful, giving only a hint at the relative amounts of leakage / capacitance from the two lines. They will probably vary according to different instruments and a low-impedance meter might not show any reading. On a floating circuit what you do not want to see is zero on one leg and the full voltage on the other, as that might indicate a short to earth.
So it’s an isolating transformer? If it is can these be modified to make the neutral true 0v?
 
Simply connect one end of the winding to earth and call it the neutral. Why do you want to change it? Have you considered why it is arranged this way now? Is anything depending on the electrical separation for safe operation?
 
So it’s an isolating transformer? If it is can these be modified to make the neutral true 0v?
Simply connect one end of the winding to earth and call it the neutral. Why do you want to change it? Have you considered why it is arranged this way now? Is anything depending on the electrical separation for safe operation?
It’s simply just a transformer for a control circuit that runs 2 three phase motors for an extraction system it’s industrial so can’t see any reason why it has to be isolating. I’m don’t know weather I’m being silly hear but I thought with isolating transformer I shouldn’t pick up a voltage to earth? Just between each end of the transformer winding?
 
Well that would be true if there were exactly zero leakage and zero capacitance to earth. But even before you start to run cables from it, the transformer secondary has capacitance to earth, through which a small amount of AC can flow to give a reading on the meter. The more cabling and equipment, the more leakage can flow. It's a ghost voltage if you like that term, that will probably go away if you use a low-impedance tester.

Floating circuits are single-fault tolerant, and can reduce the voltage and leakage in critical places where insulation is challenged. Don't change the configuration simply because you 'like' one wire to be neutral!
 
Well that would be true if there were exactly zero leakage and zero capacitance to earth. But even before you start to run cables from it, the transformer secondary has capacitance to earth, through which a small amount of AC can flow to give a reading on the meter. The more cabling and equipment, the more leakage can flow. It's a ghost voltage if you like that term, that will probably go away if you use a low-impedance tester.

Floating circuits are single-fault tolerant, and can reduce the voltage and leakage in critical places where insulation is challenged. Don't change the configuration simply because you 'like' one wire to be neutral!
Interesting but if it was earthed I can’t see the problem from a safety point? With isolating transfers what’s to protect us on the second fault?
 
It looks to be in a control panel so as above, it's been designed by someone who wanted it the way it is, don't change it unless you have a good reason and know exactly what the consequences are.

Have you notice the earth wire in the terminal block, presumably not connected, but what's happening before the block?
 
I’m just confused how to tell if it’s an isolating transformer by measurement? And the idea of a second fault on these type of transformer what’s in place to stop us getting a shock on the second earth fault?
 
As Lucien says, it's an ISOLATING transformer, with an earthed screen between the windings to ensure it stays isolating in the case of transformer failure.
If you connect anything from the supply side to the secondary, including earth it is no longer isolating.
Any fault to earth anywhere on the secondary side, or what's connected to it, can only produce a maximum of 110 volts to earth at any point, which should be non lethal. If you get a second fault to earth at any point, other than one that is at the same potential as the first fault, then the fuse blows.
 
JAko13!: Good morning. A good observation which shows you are thinking about your electrical measurements and what they mean or tell you.

I have drawn the circuitry for a perfectly isolated secondary side; why does the meter read 0 V or better - why is the meter current I zero Amps - when the meter lead touches either L1, L2 , L3 or L4?
 

Attachments

  • [ElectriciansForums.net] Transformer neutral reading 28v
    perfect iso.png
    53.2 KB · Views: 24

Reply to Transformer neutral reading 28v in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
419
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
759
  • Question
Thanks again, I’m sure I’ll be back with many more questions
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top