I’ve seen a 110v control transformer reading 28v on the neatral to earth and 67 on the other leg. Why would this be?
 

Attachments

  • [ElectriciansForums.net] Transformer neutral reading 28v
    C174EEAD-3BAF-4E7C-BAFA-525095C3A089.png
    1.5 MB · Views: 549
Jako13!: Now study this diagram for the situation where the secondary side is imperfectly isolated from ground/earth by say insulation leakage indicated by the three pure resistors. Assume your voltmeter has a very high resistance (say 50M Ohms) which means it draws only a negligible but not zero current to take a voltage reading.

What would the voltmeter measure when connected between earth and L1, L2, L3 and L4? First though draw a circuit diagram for the upper and then the lower 110V circuits.
 

Attachments

  • [ElectriciansForums.net] Transformer neutral reading 28v
    imperfectseciso.png
    72.6 KB · Views: 26
JAko13! - Could you say a little more about these links? Pictures are helpful. This way the 'EF Brains Trust' can comment further. In the meantime I am confident you will not alter anything. What is the purpose of the panel?

:)
 
What do you mean " a Screen"?
Copper foil sheet between the primary and secondary windings. The sheet is arranged so that it doesn't form a shorted turn. Used when one winding is wound on top of the other.
The other method of making an isolation transformer is to position the windings side by side with a space between them
 
Copper foil sheet between the primary and secondary windings. The sheet is arranged so that it doesn't form a shorted turn. Used when one winding is wound on top of the other.
The other method of making an isolation transformer is to position the windings side by side with a space between them
So why do we use 110v transformers for electrical safety?
 
It might well be connected to earth at the DC side of some power supply, so really don't go changing it unless you have access to the full schematic and design details!
 
So why do we use 110v transformers for electrical safety?
There are 2 different but related aspects:

One is the danger presented by the secondary voltage itself. So you can easily kill yourself on a 240V isolated supply just but getting both ends of it, and do so without too much more difficulty on 120/110V (as US electrical accidents sadly testify to). Going down to 55-0-55 puts it out of most danger situations, unless very wet (insert joke here...)

The second danger is that of a flashover between the primary and the secondary. One traditional solution is a split-bobbin style of construction so the windings have a mm or so of solid plastic insulation and a cm or so of creapage distance between them. Another solution is to put an earthed screen between the two. This is also an advantage if electrical noise is an issue, as anyone familiar with old valve LW/MW radios will know...

That is, before all broadband modems throwing noise all over the spectrum so folk could wast time on arsebook....
 

Reply to Transformer neutral reading 28v in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
420
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Only the N side of the lamp would be at 0v if you went further along the element the voltage would rise.
Replies
14
Views
759
  • Question
Thanks again, I’m sure I’ll be back with many more questions
2
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top