Someone’s bypassed the e stop circuit so was having a look to see what they had done.What is the problem you are trying to fix? What made you take your measurements?
What do you mean " a Screen"?But it's not. 28 volts was measured, which is almost certainly not a 'real' voltage.
The wiring diagram of the Tx is visible in the OP pic., and the earth connection doesn't connect to either winding, so it's a screen.
Copper foil sheet between the primary and secondary windings. The sheet is arranged so that it doesn't form a shorted turn. Used when one winding is wound on top of the other.What do you mean " a Screen"?
So why do we use 110v transformers for electrical safety?Copper foil sheet between the primary and secondary windings. The sheet is arranged so that it doesn't form a shorted turn. Used when one winding is wound on top of the other.
The other method of making an isolation transformer is to position the windings side by side with a space between them
Site transformers produce 55-0-55 AFAIK, so with only 55 volts above earth, it's fairly difficult, but not impossible, for the average site monkey to electrocute themselves.So why do we use 110v transformers for electrical safety?
There are 2 different but related aspects:So why do we use 110v transformers for electrical safety?