I came across this installation the other day and would be interested in anyone elses thoughts on it because i consider it to be very poorly designed.
The local electricity board have just installed a new 400A TP&N supply and the electrician has used 1x150mm tri rated cable per phase and neutral to go from the cut out to his own 400A isolator. This cable is within metal trunking. From this isolator he has used 2x50mm tri rated cables in parallel per phase and neutral to a 400a changeover switch again within metal trunking. The length of trunking that these 50mm cables run through also contains standard cables rated at 70c.
I have stated to the customer that all these cables are undersized and that there will be significant issues with overheating. Not only of the cables but of the main isolator and changeover switch.
The electricians response has been that the cable rating for 50mm tri rated is 204A and therefore two in parallel is adequate for a 400A supply.
Although this is correct according to manufacturers specifications,this is for a single cable in free air with an ambient temperature of 45c. He has made no allowances for derating the cable for grouping,being within metal trunking,other cables within trunking of a lesser rating,temperature rating of main switch and changeover switch etc. As far as im concerned the 150mm is woefully undersized and that the parallel 50mm`s are even more so.
Any thoughts or additions to the above would be gratefully received because as it stands at the moment its come down to my word against his.
Neil
The local electricity board have just installed a new 400A TP&N supply and the electrician has used 1x150mm tri rated cable per phase and neutral to go from the cut out to his own 400A isolator. This cable is within metal trunking. From this isolator he has used 2x50mm tri rated cables in parallel per phase and neutral to a 400a changeover switch again within metal trunking. The length of trunking that these 50mm cables run through also contains standard cables rated at 70c.
I have stated to the customer that all these cables are undersized and that there will be significant issues with overheating. Not only of the cables but of the main isolator and changeover switch.
The electricians response has been that the cable rating for 50mm tri rated is 204A and therefore two in parallel is adequate for a 400A supply.
Although this is correct according to manufacturers specifications,this is for a single cable in free air with an ambient temperature of 45c. He has made no allowances for derating the cable for grouping,being within metal trunking,other cables within trunking of a lesser rating,temperature rating of main switch and changeover switch etc. As far as im concerned the 150mm is woefully undersized and that the parallel 50mm`s are even more so.
Any thoughts or additions to the above would be gratefully received because as it stands at the moment its come down to my word against his.
Neil