I have installed a new ring main in a kitchen extension and tested for continuity and insulation resistance before connecting to Consumer Unit. As soon as main switch turned on, even with all the MCB's switched off, the RCD tripped. I removed all the connections to the consumer unit from the new ring and the rest of the circuits were fine. So problem is with the new ring main but I can't think what the problem is. Has anyone any advice?
 
I have installed a new ring main in a kitchen extension and tested for continuity and insulation resistance before connecting to Consumer Unit. As soon as main switch turned on, even with all the MCB's switched off, the RCD tripped. I removed all the connections to the consumer unit from the new ring and the rest of the circuits were fine. So problem is with the new ring main but I can't think what the problem is. Has anyone any advice?
Anything plugged in or connected via a fused spur?
 
I have installed a new ring main in a kitchen extension and tested for continuity and insulation resistance before connecting to Consumer Unit. As soon as main switch turned on, even with all the MCB's switched off, the RCD tripped. I removed all the connections to the consumer unit from the new ring and the rest of the circuits were fine. So problem is with the new ring main but I can't think what the problem is. Has anyone any advice?
Ring Final Circuit Simon not a ring main
 

Reply to Tripping RCD on new Ring Main in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
764

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
730

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top