saying that, not all apprenticeships are equal, i was working as a sparks mate earlier this year, guy on double my wages was coming to me every 20 mins to see what to do, didnt mind helping him out as he was a road lighting sparky, only as good as what youve been taught,i should refrain from coming onto forums over weekend lol, im too mean.
 
I have installed a new ring main in a kitchen extension and tested for continuity and insulation resistance before connecting to Consumer Unit. As soon as main switch turned on, even with all the MCB's switched off, the RCD tripped. I removed all the connections to the consumer unit from the new ring and the rest of the circuits were fine

No. Both fused spurs (Saniflow and toilet floor heating) switched off.
am I missing some thing or you!
 
What do you plan to do next?

Tell us and we'll give you some pointers......
I have retested the circuit. The results for continuity are r1 0.70 Ohms, rn0.7 Ohms and r2 1.13Ohms. So far so good!
r1 + r2 sockets 0.52-0.56 Ohms. I was expecting 0.46 Ohms, so a bit high.
r1+rn are all over the place. from 0.44 up to 0.86. No pattern. Should be 0.35.
The insulation resistance are Line to Neutral ˃500 M Ohms Line to CPC ˃500 M Ohms. Sadly, the Neutral to CPC was 0.
There are only ten sockets on the ring and two fused isolators.
Can anyone suggest what is causing the problem?
 
I have retested the circuit. The results for continuity are r1 0.70 Ohms, rn0.7 Ohms and r2 1.13Ohms. So far so good!
r1 + r2 sockets 0.52-0.56 Ohms. I was expecting 0.46 Ohms, so a bit high.
r1+rn are all over the place. from 0.44 up to 0.86. No pattern. Should be 0.35.
The insulation resistance are Line to Neutral ˃500 M Ohms Line to CPC ˃500 M Ohms. Sadly, the Neutral to CPC was 0.
There are only ten sockets on the ring and two fused isolators.
Can anyone suggest what is causing the problem?
half the circuit and test both , repeat until fault traced.
 

Reply to Tripping RCD on new Ring Main in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
270
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
763
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
765

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
730

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top