I have literally just had a phone call from the customer I saw today after doing an EICR and he says one of the RCD's is now tripping every half hour or so.

There were 3 CU's in total so I am back tomorrow to finish off. I didn't have time to test each circuit on the third CU but I did find poor global IR readings (L/N - E) of 0.008MΩ.

Trip time for the RCD was 43mS.

Its a TT with a Ra of 43.4.

He is currently having the property replastered (ongoing) this could be the reason for the poor IR, but I cant understand why it is tripping now when it wasn't before. He seems like an honest chap so I believe him.

I always spend the last part of the day making sure connections are tight so I'm pretty sure thats not the problem.

I'll break the circuits down tomorrow and find the culprit, but it was more the fact thats its tripping now and (most likely) wasn't before that I can understand and could do with a few opinions?
 
I'd take a new RCD with me in the morning as said above.

I think I will do that Paul.. I was going to change the enclosure any way (standalone) as it was in poor shape!

Christ I'm done in!!

Cheers for all the information guys, feel a bit gutted at leaving an installation with a tripping RCD!
 
...And don't worry about your 500 V damaging the RCD,it will not. We know it should not be part of any 500 V test in normal procedure,but now and again,an apprentice tortures one,and it matters not...:stooge_curly:
 
I did find poor global IR readings (L/N - E) of 0.008MΩ.

8kΩ is right on the cusp of 30mA if it's L-E, and bad enough to get warm with leakage current. For that reason I'm tempted to think it's a bogus reading or N-E, but either way it's low enough to dwarf any other concerns about the RCD etc until it's found.

I work on delicate precision electronics daily and often test all over the place at 500V. I have yet to damage anything at all. As I mentioned in a related thread recently, I even test things with stickers that say 'Do not use high-voltage insulation testers'. Of course the trick is knowing the circuitry inside and the specs of components used, to be sure the test won't cause damage. But I can't remember the last time I thought to myself 'Better not test that at 500' except for surge absorbers that will clamp below 500V and spoil the test.
 
Morning all..

Just an update, albeit a pretty boring one!

I didn't end up returning to the chaps house to fault find as he rang saying the tripping was getting better. Spoke to him today and he said it has stopped.

So now I will simply get the EICR written up and let him choose if he would like to get any work done.

I hope he does as I would really like to look at those IR readings again!
 
Morning all..

Just an update, albeit a pretty boring one!

I didn't end up returning to the chaps house to fault find as he rang saying the tripping was getting better. Spoke to him today and he said it has stopped.

So now I will simply get the EICR written up and let him choose if he would like to get any work done.

I hope he does as I would really like to look at those IR readings again!

Which points at water/damp!
 
Which points at water/damp!

Yes.. But it was strange that it only started happening after I had been testing!

Also he said that the plasterer had hit a cable with their bolster (perhaps 2 days prior to my arrival) and this had tripped the RCD, that cable has now been plastered over, so that may be the culprit. When I return to do the other work needed I shall let you know! :smiley2:
 
that sounds a probable. damaged cable, wet plaster, now dried out and the plaster acting as an insulator. i'd want to start digging. it may be a potential hazard. "live" walls
 
that sounds a probable. damaged cable, wet plaster, now dried out and the plaster acting as an insulator. i'd want to start digging. it may be a potential hazard. "live" walls

The chap says he knows exactly where the plasterer went through.. I have asked him to mark it as well, just in case he forgets!

I've warned them that I may have to take off some of the plaster if the results are not satisfactory, but only after all tests have been done and all else ruled out.
 
In fact I'm supposed to be writing up the report now.. I have my cup of tea to hand and the certs right in front of me... but I'm on here! :smiley2:
 
Just giving an update..

RCD started tripping again so I returned to do some tests.

Broke down the circuits.. found the fault on one of the rings. Found the faulty point and it turned out to be one of the screws holding the face plate on a FCU was touching the neutral (where conductor was showing ever so slightly through the broken insulation). Whether or not it was me that did this I dont know, but I had certainly removed that point so when I replaced it I either nipped the neutral or at least repositioned it so that the faulty part was touching the screw!

Either way I couldn't justify any cost and had to own up to the possible error on my part, but the chap is getting me back for remedials so a good outcome in the end! :smiley2:
 
Just giving an update..

RCD started tripping again so I returned to do some tests.

Broke down the circuits.. found the fault on one of the rings. Found the faulty point and it turned out to be one of the screws holding the face plate on a FCU was touching the neutral (where conductor was showing ever so slightly through the broken insulation). Whether or not it was me that did this I dont know, but I had certainly removed that point so when I replaced it I either nipped the neutral or at least repositioned it so that the faulty part was touching the screw!

Either way I couldn't justify any cost and had to own up to the possible error on my part, but the chap is getting me back for remedials so a good outcome in the end! :smiley2:

It WAS you wot did it ... I saw you did it!!!
 

Reply to Tripping RCD since testing? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
398
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
670

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top