I have literally just had a phone call from the customer I saw today after doing an EICR and he says one of the RCD's is now tripping every half hour or so.
There were 3 CU's in total so I am back tomorrow to finish off. I didn't have time to test each circuit on the third CU but I did find poor global IR readings (L/N - E) of 0.008MΩ.
Trip time for the RCD was 43mS.
Its a TT with a Ra of 43.4.
He is currently having the property replastered (ongoing) this could be the reason for the poor IR, but I cant understand why it is tripping now when it wasn't before. He seems like an honest chap so I believe him.
I always spend the last part of the day making sure connections are tight so I'm pretty sure thats not the problem.
I'll break the circuits down tomorrow and find the culprit, but it was more the fact thats its tripping now and (most likely) wasn't before that I can understand and could do with a few opinions?