One of the RCDs keeps tripping in one of the propertys we are working on. The RCD supports the ring in the kitchen, lights and doorbell from what I can remember. when we put the ring on the other rcd in the consumer unit it didnt trip, but we need to investigate this tommorow. Any ideas whats happening. I know the purpose of a rcd is to monitor the circuits it is protecting and turn its self of if it notices a difference in current going out on the line and back on the neautral of 30mA or more.
 
Of the top of me bonce, assuming a newly installed circuit.

Visual checks (usually done during construction if working alone).
End to end continuity of conductors, using either R1+R2 method or wandering lead method (favour the first as you'll get polarity as a side effect).
Insulation resistance testing of conductors for final circuits
Polarity checks.

Then on to live testing:
Live Polarity Test.
Ze, current tests, Zs.
Then on to RCD/RCBO tests
and finally functional testing.

In practice for an existing installation you'd normally check Ze, PSSC etc

you missed out the wet finger test! :crazy:
 
doe anyone want to expain it for a simpleton. Ie go into cosumer unit and put in a temporary link between the circuit ur testing and the earth bar. get ur meter and put it on low ohm resistance setting. null leads. test between line line and cpc at each point on that circuit.

ps. as its a dead test does that mean i can get away with just tripping the main switch, or will i be best of fully isolateing things and tracking down the source which feed the consumer unit and turning that of... I think i would sooner do this but if its not necesary (sp)?
 
doe anyone want to expain it for a simpleton. Ie go into cosumer unit and put in a temporary link between the circuit ur testing and the earth bar. get ur meter and put it on low ohm resistance setting. null leads. test between line line and cpc at each point on that circuit.

ps. as its a dead test does that mean i can get away with just tripping the main switch, or will i be best of fully isolateing things and tracking down the source which feed the consumer unit and turning that of... I think i would sooner do this but if its not necesary (sp)?
Trust me....and do as TQ suggests mate as if you want to get into inspecting and testing then GN3 is the way forward....
 
Hi lofty84,im a bit worried as you have described yourself as a simpleton!!!!!!!!,now for reasons of safety if you feel that you are not competent to do testing then maybe consult your supervisor,you may be joking about your competence or then again you may be a fully qualified but alarm bells are ringing.Im getting the fact that things were just switched on before testing,the old bang/no bang method,am i missing something lol
 

Reply to Tripping RCD in the Australia area at ElectriciansForums.net

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
763
  • Question
In all likelehood, no different. The RCD on the left is looking for electricity that is going missing in action. If the total missing reached...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top