Slightly tongue in cheek title, but with all of the recent EICRs I've done, the new build flats built between 10-20 years old seem to cause the most issue for me.
Most of them have ended up satisfactory (with numerous C3s), but rarely without some adjustment or remedial work (I'm doing them for the landlords directly so I can charge all in one).
Is that general experience and proof of how fast and loose flat builders were with the regulations at that time (possibly still are), or am I just in a bad area.... (NW Kent/SE London)
The consumer units are usually either 1 RCD for everything, or RCD on socket only, they are rarely fully labelled, or labelled incorrectly. The cables are often in a mess behind the cavity so that it's hard to identify earths to lives - or they have sleeved earths together so it's a pain to ring test.
I have NEVER seen an EIC for any of the properties, though they may exist somewhere in the system I guess. Certainly none of the boards have an inspection date/retest sticker on them and the landlords have never been provided with one, even when they bought the property new.
My most recent one uncovered a heated towel rail that had been reverse wired at the FCU outside the bathroom - It was at least RCD protected since it was on the socket circuit, but that had been that way since the flat was built 15 years ago. If I'd not done R1R2 testing at every point, it wouldn't have been picked up and might not have been until it was replaced.
Being new properties they often have metal studwork too (without RCD protection on the lighting) - and they often have whatever board/mcb combination they could get a sweet deal on at the time, which sometimes means they are no longer available for replacements.
I've found that older properties are often simpler and quicker to do - if only because there are fewer circuits, and were generally done by someone competent (ignoring DIY home owners). It's been a long while since I've seen any VIR or had to fail cabling for being too old to pass IR testing.
Anyone had to do an EICR on a 5 year old property yet? would be interesting to see if they've improved...
Most of them have ended up satisfactory (with numerous C3s), but rarely without some adjustment or remedial work (I'm doing them for the landlords directly so I can charge all in one).
Is that general experience and proof of how fast and loose flat builders were with the regulations at that time (possibly still are), or am I just in a bad area.... (NW Kent/SE London)
The consumer units are usually either 1 RCD for everything, or RCD on socket only, they are rarely fully labelled, or labelled incorrectly. The cables are often in a mess behind the cavity so that it's hard to identify earths to lives - or they have sleeved earths together so it's a pain to ring test.
I have NEVER seen an EIC for any of the properties, though they may exist somewhere in the system I guess. Certainly none of the boards have an inspection date/retest sticker on them and the landlords have never been provided with one, even when they bought the property new.
My most recent one uncovered a heated towel rail that had been reverse wired at the FCU outside the bathroom - It was at least RCD protected since it was on the socket circuit, but that had been that way since the flat was built 15 years ago. If I'd not done R1R2 testing at every point, it wouldn't have been picked up and might not have been until it was replaced.
Being new properties they often have metal studwork too (without RCD protection on the lighting) - and they often have whatever board/mcb combination they could get a sweet deal on at the time, which sometimes means they are no longer available for replacements.
I've found that older properties are often simpler and quicker to do - if only because there are fewer circuits, and were generally done by someone competent (ignoring DIY home owners). It's been a long while since I've seen any VIR or had to fail cabling for being too old to pass IR testing.
Anyone had to do an EICR on a 5 year old property yet? would be interesting to see if they've improved...