Snoopdog1
Hi Guy after your best advice, been along to see a customer who is having trouble with his system which has been up and running for just over Four years and the original installers are no longer in business.
He has approx a 17kw system of Schott Asi 105 w panels on the roof Appox 162 info sketchy as limited info in handover pack, The system is wired between two SMA trip power 8kw investors. Three strings to each invertor
Both investors have the same fault and not producing energy solid red light with flashing green 3501
to me indicating low insulation resistance and SMA technical. On testing inflation resistance at 500v my lowest readings to earth are around 4meg ohms in the worst instance , so it's not great but above 200k ohms.
Sma am tell me the invertor is not compatible with those panels , but it's worked for four years. But can not give me a solution. Is their any one on here with experience with this Schott Asi panel I believe it's thin film. Any advice greatly appreciated. Thanks in anticipation
He has approx a 17kw system of Schott Asi 105 w panels on the roof Appox 162 info sketchy as limited info in handover pack, The system is wired between two SMA trip power 8kw investors. Three strings to each invertor
Both investors have the same fault and not producing energy solid red light with flashing green 3501
to me indicating low insulation resistance and SMA technical. On testing inflation resistance at 500v my lowest readings to earth are around 4meg ohms in the worst instance , so it's not great but above 200k ohms.
Sma am tell me the invertor is not compatible with those panels , but it's worked for four years. But can not give me a solution. Is their any one on here with experience with this Schott Asi panel I believe it's thin film. Any advice greatly appreciated. Thanks in anticipation