recently changed an old fuseboard to a new MK consumer unit with 2rcbo's and then RCD with 5 mcb's on it, now i IR all the circuits and all came out at <299Mohm but since day 1 the rcd has tripped whenever a high load is switched on? i tried the up and down ring and the fridge radial on 1 of the rcbo's (40A) and they worked fine but if i put them back on the rcd side they trip. anybody got any ideas? also the test button on the rcd isnt working, now this is the 2nd rcd ive tried as i changed the 1st 1 just incase that was faulty.
 
Jenions the neutral link is present in the board so that you can put more circuits on one side of the CU and use the third unlinked neutral for another RCD. Because of the circuits design you have, you only need two circuits on the first neutral bar so there is no need to use the link. If the link is left in the current in the neutral can bypass the RCD so it sees a difference in current between line and neutral current and trips. Remove the copper link and this should solve the problem.
Well that's given the game away :D
 
He could use the link. There’s a neutral bar sat there doing nothing! The neutrals could be spread out to tally with the MCB’s then. And as for the 2[SUP]nd[/SUP] MCB from the RCD what’s coming out of that?
 
annoying thing is, the rcd dont trip if you plug small loads in
Could it be a combined earth leakage issue as it only happens when sufficient load has been applied? Have you ramp tested the RCD and used an earth leakage meter to see? Possibly a certain appliance causing the issue - freezer maybe?
 
annoying thing is, the rcd dont trip if you plug small loads in
Could it be a combined earth leakage issue as it only happens when sufficient load has been applied? Have you ramp tested the RCD and used an earth leakage meter to see? Possibly a certain appliance causing the issue - freezer maybe? That's what came to my mind when you mention the IR results were ok?
 

Reply to trouble with newly installed MK c/u in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top