Hi All
i really hope someone can help, I went to replace a CU at a park home and found the earth spike that was In place wasn't even attached to the old board. When I took a Zs at the board I got a reading of 17 ohms with no earth spike. After lots of investigation it became apparent that the oil line into the property was acting as the earth. Not good!
so as part of the work I installed a new earth rod, and a 100mA type S RCD at the head of the installation before swapping the board. The reading for the new earth rod was 28ohms without the bonding connected and 18.4 with.
All seemed to be fine until the customers turned on their A/C units. Although the A/C circuits were connected to a split way CU with the 30mA RCDs the main type s RCD tripped.
They work fine with the bonding removed but obviously it can't be left like that? The installation also works fine if the A/C units are not turned on.
Any ideas would be appreciated thanks
i really hope someone can help, I went to replace a CU at a park home and found the earth spike that was In place wasn't even attached to the old board. When I took a Zs at the board I got a reading of 17 ohms with no earth spike. After lots of investigation it became apparent that the oil line into the property was acting as the earth. Not good!
so as part of the work I installed a new earth rod, and a 100mA type S RCD at the head of the installation before swapping the board. The reading for the new earth rod was 28ohms without the bonding connected and 18.4 with.
All seemed to be fine until the customers turned on their A/C units. Although the A/C circuits were connected to a split way CU with the 30mA RCDs the main type s RCD tripped.
They work fine with the bonding removed but obviously it can't be left like that? The installation also works fine if the A/C units are not turned on.
Any ideas would be appreciated thanks