solo2771
Am I right in thinking trunking(4") shouldn't be used as the only form of earthing? as I am seperating the supply meters for 2 floors in an commercial building and there is no earth going up to the first floor supply not even connected to swa armourings.
no it shouldnt be used as supply earths a seperate earth must be provided either by the armour if its size is acceptable for the purpose or a seperate earth , so you need to put one in
Sorry that is just wrong, you need to check your regs.
Trunking is OK as cpc as long as it meets the requiremetns of BS7671, there is no need for a dedicated seperate cpc conductor.
The OP needs to be more specific in what is actually being done, is he talking about a cpc or an earthing conductor?
Metal conduit can be used as an earthing conductor or cpc, trunking only as a cpc.
that's what i thought. but even as cpc i would run a separate cable in the trunking where possible.
Reply to trunking as earth in the Electrician Talk | All Countries area at ElectriciansForums.net
No mate, it was more out of curiosity than anything else. I see plenty in the high rise blocks that we fibre up that makes me cringe. See plenty...
You would treat it as a TT installation.