Hi, I am currently doing a level 2 (2365). We have been doing trunking factors and I am not sure about if you need to apply the 45% space regulation to the factor. For example, if I have trunking of 50 mm x 50 mm the trunking factor is 767. I have 1.5 mm solid thermosetting cables that have a factor of 8.6. So will the maximum number of cables I can fit into the trunking is

767/8.6 = 92

or does the trunking factor not take into account the 45% regulation and therefore, the max number of cables you can fit is

Trunking factor with 45% applied = 767 * 0.45 = 345

345/8.6 = 40 cables

So which one is correct? Does the trunking factor already account for the 45% or do you have to apply the 45% yourself?
 
Yes your trunking factor has taken into account the 45% spacing so you do not need to apply this.
Where have you got the factor of 767 for the trunking from as that seems very low for 50 × 50.
 
Upvote 0
Yes your trunking factor has taken into account the 45% spacing so you do not need to apply this.
Where have you got the factor of 767 for the trunking from as that seems very low for 50 × 50.
Thanks for clearing that up mate. The 767 is from the onsite guide, you were right it was actually for 50 mm x 38 mm trunking. Again thanks.
 
Upvote 0

Reply to Trunking Factors in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
244
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
257
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
348

Similar threads

  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
637
  • Question
As above, you really should be capable of dead testing first, as 230V is quite capable of killing or causing bad burns, etc. If you are thinking...
Replies
5
Views
985

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top