I'd prefer to see SWA instead personally. I've never seen meter tails fitted outside and I wouldn't do it, but I'm struggling to think of a regulation it would contravene if contained within galvanised steel trunking.
 
522.3.1 stipulates it shall be erected so that no damage is caused by condensation or ingress of water.

Running a cable down a wall (contained or not) and straight into an enclosure is almost guaranteed to result in the ingress of water within the enclosure (unless of course it's protected by an appropriately IP rated gland - I don't think a plastic bag fits that description). Who knows where it's going to go once it's inside. I would have run it down the side, put a U at the bottom and then go back up into the bottom of the enclosure to create a drip point.
 
Nice to see someone taking a pride in their work. However you try and tidy that up, it'll still look what it is :eek:

Would of looked less unsightly & and a better job, had the cables been installed on the inside, in trunking.
 
I have to agree with others, that looks terrible and as @SparkyChick said it would have been better entering via the bottom.
 
Thanks for the replies. Entering from the bottom of the box makes sense to me. I can't find a single property where the cable is on the outside.

It could go inside but it would be entering the grd flr flat and would have to go through a newly sound proofed ceiling.

If it was to stay on the outside, is the general consensus galv steel trunking?

Thanks

View attachment 35836
 
I might be inclined to extend that trunking the DNO have installed and use that along with the hole in the bottom of the box if you've got enough slack. At least then it will look consistent.

Just out of interest, how far away is the consumer unit once the tails go through the wall? And how are they installed inside?
 
I might be inclined to extend that trunking the DNO have installed and use that along with the hole in the bottom of the box if you've got enough slack. At least then it will look consistent.

Yes, that makes sense.

The consumer unit will be just the other side of the wall. The tails come in under the floor below where it will be placed.

Just a question of how far from the deck it needs to be placed.
 
No drip/ weather loop. Oh well to make the best of it,I would use galvo type pole capping and plenty of white mastic around the entry into the meter box.
 

Reply to Trunking in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

dreadful, I couldn't sleep at night after that install, it may just about pass but the quality of work is substandard IMO
Replies
4
Views
561
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
722

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top