Hiya lads
I was asked to have a look at wiring in a recently installed kitchen as some of the appliances tripping the rcd when on. The kitchen was supplied and fitted by one of the national companies with a bird in its title /logo (shouldn't name and shame overpriced rip off crap). The customer had also bought all the appliances ex display 7 of and 5 of them are faulty but the manufacturers engineers have stated that they are ok nothing wrong with them but ordering parts for them????. I pat tested them and found 4 x n to e faults and 1 l to e fault. Then the wiring of the kitchen. this is where I don't want to drop the guy that done it in the ÂŁ$&%.
3 x domino hobs all over 2kw each, 1 x single oven 3.6kw, 1 x int micro Combi oven 3.1kw 1 x warming drawer 2.1 kw all on the ring circuit.
The sockets the oven, micro and warming drawer all behind the appliances and plasterboard cut to allow box, faceplate and plug to be sunk in to allow appliances to go right back.
the 3.6kw oven on a 1mm flex and a 13a plug and socket.
the sockets for the domino hobs all under the plinth ( plenty of room in units )
A 6mm t&e at hobs not used. go figure
also he had worked on the heating controls, and altered lighting no rcd protection on circuits.
I have given a price for running new circuits to correctly spread the load and have isolation in accessible places, correctly connect using correct size ant type of switches, isolators etc and renew consumer unit with rcbo's but I think it is unfair for the customer to have to pay again to get done correctly but as I said don't want to drop the guy in it ( he's a commercial spark but not a very good domestic one obviously).
I don't thinks its good practice to criticise an other tradesman to a customer as if we looked hard enough we could pick fault with anything but its hard to shut up and I think he should be paying to have this fixed as he is not capable of doing the rectifications
any opinions and don't hold back
cheers
 
DITTO ! has any one approacned the previous sparky in a civilised way and asked him to rectify the faults ?
If not, then it is NOT fair to attack his character.
If the customer decides he does NOT want the previous electriacian involved ? thats a differant matter, and is NOT the previous electricians fault, as he has not had a chance to fix it !
I like how that response feels and its certainly correct legally.

However some of that stuff is so bad I'd struggle to look the fella in the eye let alone allow him another pop at doing it right.
 
I like how that response feels and its certainly correct legally.

However some of that stuff is so bad I'd struggle to look the fella in the eye let alone allow him another pop at doing it right.
As long as you are doing right Mate, suck it up and move on.
 
Ex demo appliances...sounds to me like the client was after a cheap job in the first place......and she got it
Best thing to do is give you’re honest professional judgment on the installation before touching it once you commit to the job the responsibility lies with you I’ve come across loads of jobs like this and told customer what is wrong and how to be rectified and finally the cost to do so it’s awful I know for the customer to have to pay out again but I’d rather go home and sleep without a guilty conscious knowing I done the right thing
 
Re the kitchen install, from the description given, I wouldn't be giving the original sparky consent to cross my house threshold again, let alone be given the opportunity to do the job properly as he should of done in the first place.

I would be advising the customer to have an EICR done on the electrical work. Then, dependant on the contract with the Bird people, seeking redress from them. If the client employed the tradespersons directly, then dependant on the report, consider taking the matter to a small claims court. After all, now the kitchen has been installed, its going to take more time & money to rectify.

Re the appliances, the Consumer Rights Act entitles a customer to a repair,replacement or a refund. Looks like the client has chosen repair.
 
I will email the customer a quote and let them decide
I seriously suggest that you don’t do that. I know that once you’ve started on looking at something you feel that you have some sort of responsibility to see it through. But, you didn’t cause any of this.
This is going to turn in to a bun fight. It will be a PITA, take ages and cause you sleepless nights.
I hope you have other work that you could do. Walk away.
 
I know the appliances are ex-demo but four N-E faults in 7 (presumably different) items? Out of interest, what are they? What were the readings? Is it perhaps a case of sheathed heating elements that have stood around unused and got moisture in, needing a good bake out to bring them up? Maybe that's what the appliance man meant, the items were not faulty in manufacture but for a quick fix he could change the elements?
 
This sounds like a kitchen in a large house? It was foolish to install all those appliances onto one ring and certainly not on one rcd as with by their design have leakage to earth.
 

Reply to Trying my best not to drop another spark in it in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K
Promised a photo…. Remember, this was working…. And they managed to move in without hitting it…
    • Like
Replies
4
Views
368

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top