I

impactes

Hi al,l I am working on a tt system at present. I am going to be a adding a new d/b which will be ran from an existing board which has a 30ma main switch, controlling 1 other circuit i need to change the main switch to 100ma and the 1 circuit its controlling will need changing to a 30ma rcbo as its controlling outside power and lights.
The reason i need to change the main switch is because i will be using 30ma rccbs at new db.

The question i need answering is does the 100ma rcd need to be time delayed? If so the problem i have is that its a hager board and cant seem to find a time delayed rcd from them, so is there an alternative manufacture which i will be able to use? or do they do 1 and am i just not looking in the right place?.

Also would it be advisable to put in new earth electrode to supply new d/b current Ra 25.8 ohms.

Cheers
:)
 
Hi sorry to jump back in with another question.
But was just thinking does the cable that i will be running to the new d/b not need to be 30ma protected, as once i change the rcd it will only be 100ma protected.

Many thanks
:)
 
Depends what cable it is and how it's installed. I assumed you'd already taken that into account.

Yeah apologies didn't think till afterwards, was just trying to avoid any nuisance tripping. Its a 16mm T&E and is ran in a boxing (approx 8 metres) straight from existing d/b and then is clipped direct about 600mm to new d/b. I assume from this it will need 30ma protection?.

Your advise is much appreciated
Many thanks
:)
 
Is it at any point buried in the wall i.e chased in and plastered over???

For the 600mm it is clipped direct, to what is it clipped direct to...wall surface???

If it is within a purpose made boxing and surface clipped or in mini trunking then the additional 30mA protection is not required.
 
Is it at any point buried in the wall i.e chased in and plastered over???

For the 600mm it is clipped direct, to what is it clipped direct to...wall surface???

If it is within a purpose made boxing and surface clipped or in mini trunking then the additional 30mA protection is not required.

No it is not chased into the wall and is clipped to the surface. So will be able to change it.

Many thanks
:)
 

Reply to TT 100ma Rcd + earth electrode?? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
290
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
276
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
354

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
536
  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top