Tt and tns sytem together | on ElectriciansForums

Discuss Tt and tns sytem together in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
May 19, 2011
Messages
36
Reaction score
3
Hi folks, I have issues with a job I was on today with an outside metal enclosure being bonded from a tns system and right next to it I have another metal enclosure which is bonded thought an earth pit and tt system as there are supplies to caravans protected by the tt system. My issue is the fact 2 different earthing systems are simultaneously touchable and could have different potentials, what's everyone's take on this ? Thanks
 
I would question why the caravan supplies aren't on the TNS supply?

You're right that this is not a good situation as you have two separate earth potentials in close proximity
 
I would guess that work was carried out, earthing was previously via armour of swa back to intake origin, which has since deteriorated and giving an unacceptably high efli, so they've gone TT to bypass the existing tns.

Well at least that's what I've seen contractors do before on these places when I worked on them
 
If the supply origin is common then Rod the TNS as well as leaving its earthing as is, if they come off different origins then this increases the risk of a PD between the 2 earthing set-ups.
 
Last edited by a moderator:
I would guess that work was carried out, earthing was previously via armour of swa back to intake origin, which has since deteriorated and giving an unacceptably high efli, so they've gone TT to bypass the existing tns.

Well at least that's what I've seen contractors do before on these places when I worked on them

Which is not compliant, if the SWA has deteriorated then it is unfit for continued service and should be replaced.
 
Not exactly sure why they haven't used the tns Earth, but yeah it is swa into enclosure 1 with the tns protection then a supply from enclosure 1 to the 2nd enclosure where the caravan supplies are fed from with the Earth pit adjacent.

any thoughts of a code on a condition report for this am Thinking code 2 ?
 

Reply to Tt and tns sytem together in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
695
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top