Hi.
I don't understand where the requirement for double pole comes from for fault conditions. IMHO the requirement for double pole is for isolation only - this being provided by the Main Switch.
If you look at examples of TT installations in the On Site Guide you will see only single pole cbs or rcbos.
Pete
 
Hi.
I don't understand where the requirement for double pole comes from for fault conditions. IMHO the requirement for double pole is for isolation only - this being provided by the Main Switch.
If you look at examples of TT installations in the On Site Guide you will see only single pole cbs or rcbos.
Pete

I'm with you on this one PiratePete. The requirement is for double pole isolation not double pole fault methods and like you say is provided by a main switch.
 
Why mess around with TT, especially if you're changing a consumer unit. Get the supplier out to pull the fuse, and at the same time they will convert you over to PME. Its much safer, takes minutes, and you don't have to worry about beating an earth rod all the way to the earths core to get a decent reading!
 
Why mess around with TT, especially if you're changing a consumer unit. Get the supplier out to pull the fuse, and at the same time they will convert you over to PME. Its much safer, takes minutes, and you don't have to worry about beating an earth rod all the way to the earths core to get a decent reading!


Is this for definite then?
 
Why mess around with TT, especially if you're changing a consumer unit. Get the supplier out to pull the fuse, and at the same time they will convert you over to PME. Its much safer, takes minutes, and you don't have to worry about beating an earth rod all the way to the earths core to get a decent reading!

hi all

this is not always the case, it all depends on the dno network.... several times i have applied for pme on existing tt installations and told that their network supplying the property is not multipled earthed..... so i dont think its that straight foreward.... pitty though!

regards
gary
 
You must remember that when doing an install on a tt system, both line and neutral must be disconnected in the event of a fault

You sure about that?
I think the requirement for DP dissconnection under fault conditions on a TT system is only on TP supplies (I will need to take a look in the book to confirm & its out in the van).
As already said DP dissconnection is only required for isolation & the main switch satisfies the requirement.
 
I get quite angry sometimes reading posts on TT systems on Forums. It always seems these days, that the TT system is not much more than an after thought, or some kind of supplementary back-up to an RCD or multiple RCBO devices. The most important aspect of any TT system is achieving as low a Ra figure as possible, and that may mean the installation of more than just ONE rod to achieve, as seems to be the norm these days, especially when working with unfavourable ground types or locations.

You really need a minimum value of 20ohms on any TT system to call it a ''functional'' system.( Personally i always will try and get below that value) The cable connection to the first or the single rod needs to be effectively ''Protected from the elements, and enclosed in a purpose made encloseure at ground level. The other rods of a multiple rod installation should ideally be braised or exothermically welded. If not, have the same protection afforded to them as the first rod. OH, ...and don't use the thinist and shortest rods available, you will always get better results from the bigger CSA area and longer or deeper driven rods, (sometimes achievable by rod connectors/extensions). Cable conductors should be mechanically protected by a good grade of PVC conduit or piping and be of an absolute minimum of 6mm. ....Never drive rods into the ground less than 1.5 to 2 metres from building walls, this is where the majority of the original buildings rubble will be located.

Get a TT system installed correctly, and there shouldn't be any worries of an RCD device failing, (and we all know that many DO!!) as the TT system will trip the MCB, on L-E and N-E faults maybe not as quickly as a DNO supplied earthing system, but quick enough!! Get it wrong and the installed TT system won't be capable of tripping anything....

The other thing, and a very important point is that the occupier needs to be instructed on periodic routine maintenance of the installed ground rods. So if any of you are installing TT systems you need to find out, or brush up on those maintenance procedures. Remember a well designed and installed system, should last a min of 30+ years and often much longer....

Basically, i've only scratched the surface here of installing a bona fidi TT system, there is much, much more to installing these systems than initially meets the eye!! It takes an amount of skill and experience to install a ''GOOD'' TT system...
As some have mentioned, if the supply can be converted to PME, so much the better, as TT systems for domestic installations should always be considered as a last choice, never a first choice.

In conclusion, Please never think that whacking a single rod into the ground and consider that getting under a 200ohm value is a good-un!! ...it isn't a TT system, and it certainly isn't a ''good-un''!!....
 

Reply to TT board change some pointers please in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
764
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
976

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top