A
academy
Hi all, done a cu change and periodic for a family member recently and found they had no earth supplied other than what they were getting off the gas and water main. Put a rod in for them, 84ohms, with all bonding on it drops to 0.25 ohms, even better!
They wanted the garage at the end of the garden powered up and there was an old swa 2core 4mm running to the garage. Now I know we are not supposed to export pme, so I thought even though its a tt i may as well put another rod down at the garage end, and only use the armour at one end to protect the cable, put a rod in and it is 450 ohms, put another rod on top and it drops to 430 ohms. The garage is no more than 25-30 metres from the house.
What's your thoughts on connecting both ends of the armour and doing away with the rod at the garage?
The garage is one of these concrete pre fab ones with the steel beams for the roof, I have bonded to the steel and there is no other services down there. Garage is on a 30 ma rcbo.
Also, a 2 core 4mm swa xlpe, the armouring is sufficient to use as the earth right? I have looked in gn8 at the tables for it but as I remember there is a conversion you have to do to convert it from steel to copper but as I have just finished a night shift and am typing this from my phone, I thought I would just check!
Sorry for any spelling mistakes but like I say, sending from phone, thanks in advance
They wanted the garage at the end of the garden powered up and there was an old swa 2core 4mm running to the garage. Now I know we are not supposed to export pme, so I thought even though its a tt i may as well put another rod down at the garage end, and only use the armour at one end to protect the cable, put a rod in and it is 450 ohms, put another rod on top and it drops to 430 ohms. The garage is no more than 25-30 metres from the house.
What's your thoughts on connecting both ends of the armour and doing away with the rod at the garage?
The garage is one of these concrete pre fab ones with the steel beams for the roof, I have bonded to the steel and there is no other services down there. Garage is on a 30 ma rcbo.
Also, a 2 core 4mm swa xlpe, the armouring is sufficient to use as the earth right? I have looked in gn8 at the tables for it but as I remember there is a conversion you have to do to convert it from steel to copper but as I have just finished a night shift and am typing this from my phone, I thought I would just check!
Sorry for any spelling mistakes but like I say, sending from phone, thanks in advance