Quick question, Do TT earthing systems consumer tails require RCD protection?

I believe they do, but I rarely see them on short tails? Does it only apply when the tails are over three meter?

Thanks for any help electrical masters 🙏
 
If they are over 3m then they will need circuit protection, ADS would apply therefore RCD protection is almost certainly required.
 
If they are over 3m then they will need circuit protection, ADS would apply therefore RCD protection is almost certainly required.
Westward as always you’re a hero! Can you point me to a regulation about why at 3m they require protection? Why not 2 or 4?

So shorter tails (less than 3 meters) do not require protection? Still a good idea though?
 
Quick question, Do TT earthing systems consumer tails require RCD protection?

I believe they do, but I rarely see them on short tails? Does it only apply when the tails are over three meter?

Thanks for any help electrical masters 🙏

There was an article on this suggesting RCD protection can be omitted where all outgoing circuits are protected by an RCD/RCBO providing suitable measures are in place. The tails need to be protected and supported by means of a Tails Clamp, Tail Gland and suitable support outside the enclosure. The meter tails should be stripped back only the amount which is required for termination into the main switch and not a dual RCD board (tails within dual RCD consumer units between the main switch and the RCDs are normally only single insulated cable)

 
Westward as always you’re a hero! Can you point me to a regulation about why at 3m they require protection? Why not 2 or 4?

So shorter tails (less than 3 meters) do not require protection? Still a good idea though?
434.3

434.2.1
(i) not exceed 3 m in length.

Some DNO's stipulate a maximum of 2 mtrs.
 
Last edited:

Reply to the thread, titled "TT - Consumer Tails Protection" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top