hi looking to see if you can buy new hager rcds to bs4293 s type as they have the 0.2 rather than the bs61008 0.3 disconnection time required for tt systems.
hi sorry not made myself clear
i have a tt system . the main switch is a bs61008-1 100ma type s the ze is 75ohms and the zs is 4.75 the trip time is 357m/s when teting the main rcd but the regs say it should be 0.2 for a tt. is it ok ar am i confused.com
Please check note 2 to table 41.1 you are missing the fact that this disconnection is far faults of negligible impedance, not 30mA.
Check the note and all will become clear.
I'm confused.com your Ze is 75 and yet your Zs is 4.75?hi sorry not made myself clear
i have a tt system . the main switch is a bs61008-1 100ma type s the ze is 75ohms and the zs is 4.75 the trip time is 357m/s when teting the main rcd but the regs say it should be 0.2 for a tt. is it ok ar am i confused.com
hi sorry not made myself clear
the regs say it should be 0.2 for a tt. is it ok ar am i confused.com
I'm confused.com your Ze is 75 and yet your Zs is 4.75?
seen bigger differences. Ze of 120 on TT, but Zs values coming down to under 2 ohms after connecting main bonding. obviously, the water supply pipework is a better earth than the TT rod.I'm confused.com your Ze is 75 and yet your Zs is 4.75?
but with a TT system now, under the 17th, you need a 30mA RCD, not 100mA. i suggest replacing the RCD with a 30mA 61008.