Been to look at agiving a qoute to install new bd in horse barn. Tested ze at existing socket 21 ohms. Soil floors. Concrete buildings. All done in plastic conduit, swa, rcd sockets etc. Looked at mains coming in over head. Rcd 30ma 4 pole main isolator. Tails in out to metal switched fuse, swa out of that. BUT no earth rod. So if i put in one rod to the met in the metal switched fuse and got a acceptable reading do i need to put a rod for my new board.
 
You'll need to provide a hell of a lot more information before anyone can advise you. Just a couple of questions you need to address for starters...

What's the supply (TT/PME) at the DNO service head to this farm??
You CAN'T test Ze at a circuits socket, whatever you are recording there, it sure ain't Ze!!
So where is this 21 ohm Zs/Zdb coming from, as you say there is no main earth conductor at the incoming S/fuse to this out building and there isn't any sign of a TT earth rod??

Basically you need to get your test equipment out and start investigating and testing...., then come back here with the results. Simply banging in an earth rod isn't necessarily going to sort your problem, if indeed you have one!!
 
Zs = 21 ohms at a socket on db.( my mistake before calling it ze) 3 phase tt supply. No earth rod. Supply goes from rcd main switch to metal clase switched fuse. Swa then across yard to db in a shed. Did notice where db was that the steel work of building was bonded, so i think this would be giving a low reading. So if i put rod at mains and get a low reading do i need to put one at every board even if i get a low reading. Thanks
 
Zs = 21 ohms at a socket on db.( my mistake before calling it ze) 3 phase tt supply. No earth rod. Supply goes from rcd main switch to metal clase switched fuse. Swa then across yard to db in a shed. Did notice where db was that the steel work of building was bonded, so i think this would be giving a low reading. So if i put rod at mains and get a low reading do i need to put one at every board even if i get a low reading. Thanks
You can't work from a Zs, you need to take a Ze reading at the MET!!
 
So if i put rod at mains and get a low reading do i need to put one at every board even if i get a low reading. Thanks

What are the soil conditions like? What are you expecting one rod to achieve? What do you consider to be a low reading? Some daft people would consider the 21ohms you have already to be a low reading! What sort of fault currents are you expecting the rods to have to handle?
 

Reply to tt earthing on farm in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
754

Similar threads

  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
703
You would treat it as a TT installation.
2
Replies
29
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top