Hello
Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January.
Existing is a TT system with a solar installation fitted.
Current install has a 100A TP incomer, meter, C63 TP MCB, solar install, 100ma RCD, distribution board fitted with more MCBs than there are RCBOs.
Please see photo attached.
I have no experience with solar installations. Am i “allowed” to relocate the enclosures and shorten the tails going to them?
Can these tails be covered by my new proposed 100A 100mA time delay RCD or is there a reason they haven’t already been by the previous installer - something in the regs relating to this maybe?
Proposing to go from the meter to a 100A 100mA switch, then to solar, then to new DB with 30mA protected circuits throughout.
There’s a few three phase circuits but nothing requiring additional protection (cables supply air conditioning and refrigeration condensing units and not hidden within walls, no sockets etc etc) so going to omit the 30mA protection from these.
Look forward to your input.
Thanks
Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January.
Existing is a TT system with a solar installation fitted.
Current install has a 100A TP incomer, meter, C63 TP MCB, solar install, 100ma RCD, distribution board fitted with more MCBs than there are RCBOs.
Please see photo attached.
I have no experience with solar installations. Am i “allowed” to relocate the enclosures and shorten the tails going to them?
Can these tails be covered by my new proposed 100A 100mA time delay RCD or is there a reason they haven’t already been by the previous installer - something in the regs relating to this maybe?
Proposing to go from the meter to a 100A 100mA switch, then to solar, then to new DB with 30mA protected circuits throughout.
There’s a few three phase circuits but nothing requiring additional protection (cables supply air conditioning and refrigeration condensing units and not hidden within walls, no sockets etc etc) so going to omit the 30mA protection from these.
Look forward to your input.
Thanks