GLENNSPARK

well...here I am again...this time its installing a TT system utilising 2X 5/8" rods...with the connector..:

Picture 002.jpg
here is the necessary gear as laid out (the 20mm PVC conny isn`t in the pic)

Picture 001.jpg
these are the type of rods you need...no 3/8" twigs here (apart from in that bush behind maybe)

Picture 003.jpg
site is about 1 1/2 meters away from the house...thats the first one in..now to connect the second onto the first ....and carry on...

Picture 004.jpg
still some way to go...

Picture 005.jpg
get it brayed in....Robert my assistant uses the fork with a bit of tape to keep the rod steady

Picture 006.jpg
thats a length of 10mm CSA G/Y being pulled through a length of conny for main earthing (the conny was dropped into the ground)

Ze was OK at just over 15 ohms...had to change the 16th edition setup in the board...it was configured as a split load 10 & 2....dropped another RCD in it and did it 5 & 5
happy days...:biggrin:
 
I think everyone knows where I stand on this. For those who don't, either install as many rods as neccessary to achieve a stable TN value or rely on an RCD. There is no inbetween and anyone who bleats on about how they got 10ohms and that's how it should be done is a fool! Your 10 ohms is just as good as my 500ohms as we'll both more than likely be relying on an RCD rated at 30mA and a type-s on the distribution circuit.

That's my two pence anyway, I say no more other than to say WP, I'm with you buddy :)

If you really believe that, then it's not us that is the fool!!

That's what buddy's are for!! lol!!
 
OK that was an intended insult.

I’ve only been industrial and the only domestic TT install I’ve done was my own house*.
0.65 Ώ for the earth nest in the back yard. Lower when I altered it (it went way beyond the back yard!)

With industrial MV/LV substation installs we would be looking for < 0.5 Ώ.
1 Ώ being the limit for solid MV/LV earth interconnection.
>1 Ώ <5 Ώ and we had to operate an isolated earth where two nests were needed. That never happened as we would sink bore holes if needed to lower the LV earth values to <1Ώ.

Victoria centre in Nottingham the then EMEB had to drill 30m bore holes to form a nest in the Bunter Sandstone to get a good reading (at 30m it would be well below the water table.)

* I was an apprentice and buying my first house. Anything you wanted that was scrap you could buy for a pittance. I demolished an 11KV substation, copper lattice earth mat £1-00! The best bit, the then electrical senior engineer arrived with all the companies gear to test it.
 
There are clearly two totally opposite camps here.
My view is clearly the minority but I have some support from respected member Mr Skelton. I have also had support via PM from another respected member who understandably doesnt want to get involved in a slanging match with See you next tuesday who's above reply I havent bothered reading.
Based on that and the historic support by IQ,who sadly doesnt post much now,I know I'm not wrong,just take a different view.


Skelton summed it up nicely, get a stable TN value if you wont rely on RCD 's for ADS....,whats the point otherwise of a stable 10-15-21 ohms?.....if a reading of 50 ohms,or a 100 ohms is stable whats the difference?
 
If you really believe that, then it's not us that is the fool!!

50V/10ohms = 5A fault current. Will this trip an OCPD? No. Will this trip a type-s? Yes. Will this trip a 30mA RCD? Yes.

50V/500ohms = 100mA fault current. Will this trip an OCPD? No. Will this trip a type-s? Yes. Will this trip a 30mA RCD? Yes.

See my point? There aint no difference!

Eng, I respect your opinion, I just think it's wrong.
 
Dear oh dear oh dear, it seems that the importance of Stability on a TT system is clearly very misunderstood by some here!! Perhaps i can suggest that some reading is called for here.

I find It amusing that around 18 months ago, when i was advocating very similar measures to that of Outspoken, i was bombarded and ridiculed by the very same people, ....then it was filling a garden with copper!! Now it seems, all has changed and something to be applauded, even though they wouldn't ever contemplate doing anything like it themselves!! lol!! Well i'm all for going all out to achieve TN values, so is the other camp going to change their mind again now?? lol!!

I've been involved with TT systems for more years than i care to remember as well as passive cathodic protection systems using just about every type of electrodes and method you care to mention. Even my own house in Cyprus is a TT system (0.89ohm overall and still improving) There are many ways to achieve sub or very near 1 ohm values in most soil/ground conditions, with just two or three of your short 1.2m earth rods, but unfortunately for some, you need to put a little effort and some extra cash into achieving it!! Let's say you achieved a value of 1 or 2 ohms with 3 rods, would you or wouldn't you add another rod?? You see for me, that situation would be a no-brainer, but for the other camp it would be ...Why Bother i've got my 30mA RCD!!!


Basically i have no time for those that can't or don't want to be bothered, but always seem to find it necessary to ridicule those that are. The very fact that a TT system should be installed to provide a 30 year lifespan and are often still in place far longer, doesn't seem to mean anything to them either. No wonder standards in the UK overall, are falling at the rate they are. Makes you wonder why they even bother with installing a TT system at all, when they can rely on a RCD to cover their arse, .....well it was OK when i left it 5 years ago mate!!


And it's ME that's wrong!! I don't think so!!
 
achieving TN values is good, think wirepuller and most other members will agree. point WP has been making is that if TT values are above 1 or 2 ohms, then they are not really any better than 100 ohms. as OCPDs will not provide adequate fault protection.
 
achieving TN values is good, think wirepuller and most other members will agree. point WP has been making is that if TT values are above 1 or 2 ohms, then they are not really any better than 100 ohms. as OCPDs will not provide adequate fault protection.

Read past threads Tel, pointless to use all that copper according to WP around 18 months ago. We all know the draw backs of too higher a Ra value, but were normally talking more about Stability issues when talking about installing two X 1.2m, which as a consequence, will also in many circumstances provide around a 10 ohm Ra value!! But then it seems that stability is also not worth worrying about either!! lol!!

1 or 2 ohms, or lower single figure values, will give a far better protection level than 100 ohms. May not disconnect some OCPD's in specified times, but will trip, unlike a RCD with a reliability problem....

This dispute is all about those that are prepared to put the effort in to providing a good TT system, and those that are just not!! What annoys me, is that the can't be arsed, then find the need to high jack threads and ridicule those that do want to make an effort to do a good job.
 
achieving TN values is good, think wirepuller and most other members will agree. point WP has been making is that if TT values are above 1 or 2 ohms, then they are not really any better than 100 ohms. as OCPDs will not provide adequate fault protection.

That is exactly my point.
Having against my better judgement read post 86 let me respond by stating that yes,there was a time when I didnt think TN values were obtainable by normal rodding methods. If anyone cares to trawl through more recent posts though you will find that I have no quibble with those who wont accept an RCD as an earth fault device,and insist on TN values of Ra and go the extra mile to get them. Nobody who uses this forum regularly over time can fail to be influenced by other opinions and the wealth of experience on here,and I have seen that values of Ra in line with TN values are possibly obtainable. But for the few small scale TT projects I do (sheds/small construction site units etc) I dont think it is worth 'filling a garden with copper' to acheive it,I am happy to adopt the 7671 preferred method of earth fault protection...RCD's (411.5.2 (i) ) and not start banging in rod after rod after rod.
If post 86 is 'all for going all out to achieve TN values' why the f*** is he having an orgasm over 15 ohms in post 24?

While I have the utmost respect for Glennspark and Tel's opinions on this,(and I would have for E's if he wasnt such an arrogant ****) nothing and nobody will ever convince me that 15 ohms is to be applauded and 150 to be ridiculed. It doesnt stack up.Nobody will ever convince me either that stability is that important for 'non-TN readings'...(15 ohms? 21 ohms ffs?) or that the only way to achieve it is to go down halfway to australia.There are a number of regular clients of ours with long standing TT installations served by 4ft rods where we carry out regular maintenance/small installs ,and the readings never vary,summer or winter.
 
That is exactly my point.
Having against my better judgement read post 86 let me respond by stating that yes,there was a time when I didnt think TN values were obtainable by normal rodding methods. If anyone cares to trawl through more recent posts though you will find that I have no quibble with those who wont accept an RCD as an earth fault device,and insist on TN values of Ra and go the extra mile to get them. Nobody who uses this forum regularly over time can fail to be influenced by other opinions and the wealth of experience on here,and I have seen that values of Ra in line with TN values are possibly obtainable. But for the few small scale TT projects I do (sheds/small construction site units etc) I dont think it is worth 'filling a garden with copper' to acheive it,I am happy to adopt the 7671 preferred method of earth fault protection...RCD's (411.5.2 (i) ) and not start banging in rod after rod after rod.
If post 86 is 'all for going all out to achieve TN values' why the f*** is he having an orgasm over 15 ohms in post 24?

While I have the utmost respect for Glennspark and Tel's opinions on this,(and I would have for E's if he wasnt such an arrogant ****) nothing and nobody will ever convince me that 15 ohms is to be applauded and 150 to be ridiculed. It doesnt stack up.Nobody will ever convince me either that stability is that important for 'non-TN readings'...(15 ohms? 21 ohms ffs?) or that the only way to achieve it is to go down halfway to australia.There are a number of regular clients of ours with long standing TT installations served by 4ft rods where we carry out regular maintenance/small installs ,and the readings never vary,summer or winter.


Arrogance or lack of, it has nothing to do with it, my stance has been the same throughout!! You can swear all you like, but ridiculing those that want to do things properly or better, that you find pointless isn't helpful to anyone, end of!! No-one's trying to convince you of anything, it's up to you to do your own research, ...and no-one is particularly applauding or ridiculing 15ohm/150ohms, that's just you seeing what you want to see!! I don't see how driving two or three 1.2m rods is going halfway to Australia. If you've been in the industry for 35 years, you would know that 2.4m and 3.6m are basically the same as what used to be the Standard sized rods in the UK, and still are in most other countries!!

No ones having orgasms, that's just you trying to emphasize your less than clever ridicule!!

As for your statement on 4 foot rods (which are probably twigs), I don't believe a word of it, not unless you have somehow changed the law of physics, especially in the UK's seasonal weather conditions!! A 4' rod having a certain ohmic value in the height of summer, will not have the same or even near ohmic value in the height of a freezing winter with snow on the ground, ....and that is an electrical Fact!! And is why depth and stability is, and always has been key to any TT roded system....


You stick to your BS 7671 (411) and continue to do as little as possible, and leave others to do Better!!
 
The electrical supply company don't supply an earth point in 99% of cases anywhere on the Island!!!
Not seen any evidence of TT systems in the north, are you referring to the the south as 'the electrical supply company' in the north is government owned and clearly don't regulate the south?
 
Not seen any evidence of TT systems in the north, are you referring to the the south as 'the electrical supply company' in the north is government owned and clearly don't regulate the south?

Yes my house is in the South and the supply company is also basically government owned. But the North would have been under the same company prior to the invasion, so unless something has radically changed since that time, i would suspect the same would apply to the North, and that TT systems are the norm... You know what the Cyp's are like when it comes to spending money, that they can't see any return for!! ...lol!!
 
Yes my house is in the South and the supply company is also basically government owned. But the North would have been under the same company prior to the invasion, so unless something has radically changed since that time, i would suspect the same would apply to the North, and that TT systems are the norm... You know what the Cyp's are like when it comes to spending money, that they can't see any return for!! ...lol!!
Ah OK, (I'll not bite on the issue of Greek propaganda). The standard of wiring in the north is atrocious - saw this today whilst out running
IMG_3464.jpg
 
i think just to summerise this
I will have a chat with delroy (my boss)....and if he OKs it I will send another rod in....
theres no reason why he shouldn`t...but I have of course to run it all by him first...
thats the way it is...
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
TT...installing 5/8" rods
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
98
Unsolved
--

Advert

Thread statistics

Created
GLENNSPARK,
Last reply from
guest119,
Replies
98
Views
9,841

Advert

Back
Top