200A 3phase tt system with metal clad control panel no rcd at origin 4pole main switch. I have always put rcd at origin but it has been put to me if you can prove a very stable low Ra (ze acceptable) rcd may omitted? What is an acceptable low level and how can you prove it will stay stable. No testing has been done yet was ,there to price another job this was me being nosey at origin. Thoughts please
 
to omit the RCD, you need a PEFC large enough to operate the OCPD within specified timescale. a Ra value >1 ohm will not achieve this.
 
A 200A BS88 will need about 1800A to blow within 1s so an RA of <0.12 Ω would achieve this, if the earthing method has been in place for along time and not varied it is stable, if the earthing system is below the variations of the changes in ground temperature during the seasons and the ground has settled around the earthing system then the earth should be stable long term.
 

Reply to Tt no rcd at origin in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
694
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top