Joined
Jun 2, 2017
Messages
14
Reaction score
1
Location
London
Hi guys came across this today, Ze of 37 ohms, surprised me as thought it was a tncs- Victorian house, Db from 1989, no docs- could it be a TT off the water main? 10mm bonding to gas and another 10mm out of sight. The met on the rhs of tncs
block not connected to neutral- can anyone help me with some ideas? Cheers.
[ElectriciansForums.net] TT off water main or tncs with no earth (Victorian house city centre)
[ElectriciansForums.net] TT off water main or tncs with no earth (Victorian house city centre)
 
Yes, last sentence of 542.2.6 -Other metallic water supply pipework shall not be used as an earth electrode unless precautions are taken against its removal and it has been considered for such a use.
So it can be used.
 
200 Ohms is the value recommended not to be exceeded in regs, as you well kn0w . Yes NICEIC do recommend under 100. For an earth electrode. So far as the nonsense is concerned(I'll be objective here not obstructive)If you look at B.S.7430 IT RECOMMENDS 100 ohms max and 2 meters of rod as the top meter of soil can be unreliable. Eh?
542.2.6 Says other metallic water supply work can't be used unless
precautions are taken and it's been considered for use. So if you'r
desperate and can understand what that means, and what ''Other''
is and you can be bothered with all the hassel , you can. Maybe.
 

Reply to TT off water main or tncs with no earth (Victorian house city centre) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
I must say as well that I can only get a loop reading on the two wire hi setting, on the 3 wire low the readings are all over the place from <0.01...
Replies
5
Views
2K
  • Question
Indeed it is clearly marked as a PME earthing system, which means it is TNCS.
Replies
5
Views
3K
loz2754
L
  • Question
It is a TNS system, the earth rod is providing an earth reference to make on epile of the supply neutral and is not part of the earth fault loop...
Replies
20
Views
5K
davesparks
D
Thanks Dave, I appreciate the reply as I knew it was something I wasn’t picking up.I’ll read up in the regs book on an IT supply as Can’t say I’ve...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks