Evening guys, I've got 2 basement rooms that are being supplied from their own cu which is fed from a 32A MCB in a split load rcd board in the house which is a TT installation. The cu in the basement is relying on the CPC in the 6mm supply cable to the basement cu as its main earthing conductor. The cu in basement has a lighting and socket circuit. With no rcd protection but is rcd protected back in the house cu.Do I need to install a rod for the basement cu and does it need rcd protection?Thanks
 
if the 32A breaker feeding it is RCD protected, no need to fit another one. as for a second rod, you can fit 1 if you want. it may bring the overall Ze down.
 
Last edited:
Thanks Telectrix, I've got to knock a deeper rod in for the main cu ( getting a reading of 225 Ohms ) So the 2,5mm CPC in the supply cable to basement cu is acceptable to act as the main earthing conductor for the basement cu?
 
to determine that, you would have to know the Ze and PEFC. then apply the adiabatic equation. generally for a TT system, 2.5mm is adequate, unless you can bring your Ze down low. say you got your Ze down to 23ohms, that would give you a pefc of 10A, for which 2.5mm is adequate .
 
Last edited:

Reply to TT on DB number 2 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
311
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
936

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
Haha yes, it is. Must be a northern expression. Have a Google 😂
Replies
3
Views
318

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top