L

lionelmcc

Hi
I was looking at a job the other day which had a recent minor works cert which had the arrangement down as TT.
On further invesigation I discovered that the 16mm earth cable did indeed leave the building but went up the wall outside and was connected into a 3 wire overhead supply.
I am presuming this is TNS or am I barking up the wrong wall?

L
 
I have never seen that done either, something not quite right there, the DNO don,t run earth wires to there overheads, they usually are pme at the cut out, they are around here anyway.
 
Ok, I'll investigate further and keep you all posted

I have never seen that done either, something not quite right there, the DNO don,t run earth wires to there overheads, they usually are pme at the cut out, they are around here anyway.
I will contact the suppliers on Monday, however I have just been back to the site and followed the poles back a few hundred yards, until it disappeared into wood.
The house is an old gate lodge for to a larger house, which I am also looking at doing some work on.
The big house would appear to be supplied by the same method and, on looking inside would at first glance, seem to have a PME arrangement although there is no PME label at the main fuse or meter.
also , when driving home I did notice lots of poles ( all over the place) with three wires

I feel Like I am on a different planet
 
Last edited by a moderator:
Hia mate, the only time i have seen anything of the like is when the DNO has brought there own earth off the pole to an earth rod or plate near their pole, but never back into a dwelling or such like, interesting though what u have said.
 
Hey.

Des seems to have the most logical opinion. But then that 3rd wire could also form part of a TN-S system, depends where and how the other end is connected

Very difficult to tell really.:confused:
 
i followed the poles back for about 400 yds until they crossed a stream and on into the woods
then walked on to the house which has the same arrangement with the wires coming back accross from a different part of the woods
it's difficult walking country
 
Ok the plot thickens

I took a reading fo Ze; 0.46. Would suggest PME?

when I phoned he DNO (Scottish Power) I was told that they did not have that information.
I was then condescendingly told by some jumped up receptionist, that, "Any electrician worth his salt would be able to tell"
At this point I am glad that I am not the only person on this forum who is confused

Comments please

L
 
Hi
I was looking at a job the other day which had a recent minor works cert which had the arrangement down as TT.
On further invesigation I discovered that the 16mm earth cable did indeed leave the building but went up the wall outside and was connected into a 3 wire overhead supply.
I am presuming this is TNS or am I barking up the wrong wall?


L
sounds pretty obviously a TN-S.Separate earth throughout.Your ZE reading is also too high for TN-cs.
The suppliers have moved away from using these systems nowadays due to economical reasons and safety(cost of extra cable,and possibility of gypos stealing it for scrap) But as it is a pretty old installation by the sound of it TN-S sounds favourate.
 
Hi jason

I disconnected the bonding and tested between the incoming earth and the henly from the L tail

What about the attitude of the DNO?

Im afraid its the luck of the draw who you get when phoning them.

You could try phoning back and asking to speak to someone more in the know. They are there.

Remember, when you call them, the people that answer the phone do not have a lot of technical knowledge.

I struggle when i phone to book a PME enquiry.

Is there any way you can get us some pics?
 

Reply to tt or tns? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
808
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
981
Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
857

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top