just testing an install for my pending inspection and doing the testing as per onsite guide so do it in correct sequence and im doing my pfc checks and have to low readings,
L to N 0.47 kA acceptable
L to E 93 A is this acceptable and normal?
am i being a doyle and forgetting something here?
its a tt system a fair distance from a village so a good long run from substation
no ideas anyone?
L-N takes your breaker out and has to be high enough
L-E will operate the RCD 230/93=2.47 ohms max Zs=1667 for 30mA & 500ohms for 100mA
you have 93amp
Kev
no ideas anyone?
Can I ask what was the supply voltage and what rating and type of protective device at the origin, also what is the largest fuse or Circuit breaker in the CCU.
Hi Matt
With TT systems you will get low PFC so what you do is RCD everything. Basically the MCB,Fuse it OVERLOAD protection only and the RCD is the FAULT protection.
When testing prove tripping times on the RCD you probbably wont get them on the MCB or fuse.
As for your maximum ZSn values remember to think about your touch voltage which has to be less than 50vAC and use the formula I delta n x Zs <50v
I delta n is tripping curret of the RCD so 30ma in this case
If you`re not familiar with TT`s the PEFC`s can be worrying until you do the maths - then you realise why RCD`s are so necessary with TT.
Assuming single phase @230v then Z-LN (impedance of Line to Neutral) would be 230v / 0.47KA = 0.48 ohms, which is relatively high but understandable due to the run from tx.
If you check out your trip curves in BS you`ll see that 470A is enough to pop all your type B`s (assuming it`s a new install) upto 100A.
Then on the EFLI side...
Ra (aka Ze) would equal 230v / 93A = 2.5 ish ohms - so you`ve done good with your rod(s)
Then, remember Ra x I^n < 50v (safe touch voltage)
So your Ra (Ze) of 2.5 x 0.030A = 0.075 (a very lowly 75 milli-volts - a very safe touch voltage :))
Even if you`ve kept the 100mA front ender for some ccts that`ll give 250mV (2.5 x 0.100)
Understandable that your anxious for your assessment, but on those figures you can relax a little ;)
Matt just a quick question when you took your ZE did you have a full shut down and isolate the installation take a true ZE or is it a ZE(DB)?
If so you will need to prove your rod reading as you have got earth paths throught your pipework and metalwork which may give you an falsly low reading.
Ah bagger, just realised 3 of you have already replied...
Sorry for repeating what you already said :eek:
i fink that last drink has gone to me burp head
Totally wi` you big Scotsman.
a bit out of balance readings considereing Z LN so high but suspiciously low Ze
Tink your question well worth asking - don`t want the guy to mess up due to what i said, sure hyour the same
hi,
i tested the installation with the earth attached to the cu, then i tested the earth electrod resistance which is 120ohms
(it has been raining quite heavily )
voltage at source is 246V
voltage is 246
largest mcb in cu is 32A
boards fuse 1361 type 11a 60A
cheers matt
Also which reading do i put for pfc on the test sheet?
thanks everyone for their help!
matt
Matt, are you saying it had been raining heavily when you got 120 ohms ?
& who`s the inspection with ?
Did you follow the explanations of the numbers you`d got?
inspection is with niceic!
it had been raining heavily, just had a look where the stake is there is a weed sheet underneath gravel so it is dry under there!
Yeah ran through the calcs did them myself to get up to speed with it again
which value do i record for the pfc the L-n value?
Is it not the case that the NICe insist on 100 ohms or less then?
Not with em meself but i `thought` that was the case - is there a bit of leeway shown - i.e. must be below 200 but `like` you to achieve 100 or less :confused:
& as Scotsparky said it`ll be your PEFC you`ll record in this case - cos that`s the greater of the 2 PFC `s
Reply to TT PFC question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...