Surely it would be PSCC that is the highest, at 470A, not the PEFC at 93A? Or have I missed something silly.... :confused:

No, i don`t think you have :):confused::)

You`re quite correct if you`re saying that the PSCC will be filed as the PFC.

The OPs confusion was due (i`m assuming) to the very low PEFC values TT installs throw up. Hence the discussion :D

or atleast i thought thats what we were discussing :p
 
Oh, it was only because he was asking which one to put down as the PFC value a couple of posts back, and you both said the PEFC.... Didn't want him to get a cross against something in his inspection by putting down the 93A value on his paperwork. Although with a Ra of 120 ohms it's gonna be a lot lot smaller than 93A.

I'm think I'm confused by the whole discussion, if I am please just ignore me and I'll go sit in the corner. :eek:
 
Oh, it was only because he was asking which one to put down as the PFC value a couple of posts back, and you both said the PEFC....
I'm think I'm confused by the whole discussion, if I am please just ignore me and I'll go sit in the corner. :eek:

Umm... don`t think anyone did actually :confused:

Maybe i`m confused -think i`ll join you in the corner :D
 
i was looking for which value to put in the pfc box on the IET websites EIC certificate
0.47 ka was the reading L-N and 93A was the reading L- E
im a little confused as its been a while since i tested a tt system so hence a little confusion over the readings!!
 
Ah, so that's where the confusion has come into the discussion... On my part anyway.

I was always taught to put the highest of the PFC's into the box!

Would the worst case scenario not be the higher of the two?
 
Worse case woulf =ld be High ZE and low PFC remamber you want a high fault current for your disconnection times. so if its lower then slower disconnection times.
 
I understand what you're saying completely, but I am going by what is written in GN3. I only have the 16th edition copy with me at the mo, but it states that "Prospective fault current (PFC) - The value recorded is the greater of either the short-circuit current or the earth fault current. Preferably determined by enquiry of the distributor"

Damn, I sound really arsey for a new poster on here but I don't mean to be. But like I said, I don't want the fella to get marked down on his NIC assessment.
 

Reply to TT PFC question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top