Evening poeple. Could one of you fine chaps tell me where i'm going wrong please:confused:

I measured an Ra of 98.3ohms on a install, so worked this out to be 2.34amps PEFC. When I use my meter to fing the PEFC, its giving a reading of 0.64kA.

Is it me being stupid and totally missing something here:eek:
 
Spooky....

Deffo no bonding? or cross connection with neutral anywhere?

Cant even imagine how you would get such a result !


No bonding anywhere. Main switch was open during test so if there was a cross connection it shouldn't have made a difference.

I'm baffled. Will still use the worked figure for the Ra, just wish I hadn't checked it with me meter now. Paranoid:mad:
 
Evening poeple. Could one of you fine chaps tell me where i'm going wrong please:confused:

I measured an Ra of 98.3ohms on a install, so worked this out to be 2.34amps PEFC. When I use my meter to fing the PEFC, its giving a reading of 0.64kA.

Is it me being stupid and totally missing something here:eek:


Sorry to sound really dumb but what does Ra stand for?? Is it the same as Ze but called Ra on a TT system??

Thanks
 
But then, I suppose you must have disconnected the the main earth and are testing purely the earth electrode....

Please investigate.... I need to know :D
 
But then, I suppose you must have disconnected the the main earth and are testing purely the earth electrode....

Please investigate.... I need to know :D

Main earth conductor disconnected from earth bar, then testing between that and the incoming line on the main switch,(main switch open of course)

I will be finding what caused it as its stuck now in the back of my mind and will be for ever i think.

Test meters fine, as using it all day every day and all results are fine.

Will be back there friday anyway so will test again. Wouldn't mind, but the Megger is so simple to use so its not as though i've messed up setting it up:mad:
 
Sorry to sound really dumb but what does Ra stand for?? Is it the same as Ze but called Ra on a TT system??

Thanks

Basically yes - it is usually defined as the total resistance of the electrode/rod and the protective conductor connecting it to exposed conductive parts, but obviously it is the earth electrode that has the most significant contribution to it.
 

Reply to TT Ra assistance in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
570
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
999
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
938

Similar threads

I am with you. Their RCD did not comply with the standard. The only one I know that does comply, though I am sure it isn't alone, is the Garo...
    • Like
Replies
10
Views
775
I would hazard a guess your electrician may be able to contact your DNO and have the switch swapped to a MFS very quickly..
Replies
13
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top