TT stake in outbuilding

Discuss TT stake in outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
Evening. Came across a shed with armoured 2 core 2.5mm running to it on a TNCS system (RCd protected), with the sheath of the armoured being used as the earth (Shed is only 5m from house); I know this can be acceptable, but I’m adding sockets in the garden and was considering putting in an earth stake along with a new CU in the garage to split the sockets and lights etc. There is no metal pipework or roof etc in the shed.
1. Would you leave the existing earthing arrangement (which is giving current Zs of 0.6) which uses the metal sheath of the armoured cable or put in a stake which might will probably have poorer readings?
2. If you put in a stake, what size should the cable running to it be, and where do I find this in the regs?
 
Evening. Came across a shed with armoured 2 core 2.5mm running to it on a TNCS system (RCd protected), with the sheath of the armoured being used as the earth (Shed is only 5m from house); I know this can be acceptable, but I’m adding sockets in the garden and was considering putting in an earth stake along with a new CU in the garage to split the sockets and lights etc. There is no metal pipework or roof etc in the shed.
1. Would you leave the existing earthing arrangement (which is giving current Zs of 0.6) which uses the metal sheath of the armoured cable or put in a stake which might will probably have poorer readings?
2. If you put in a stake, what size should the cable running to it be, and where do I find this in the regs?
Yes there would if the W/S /Shed has any metalwork that would require bonding, and the CSA of the armouring wasn't large enough to cope with earthing and any bonding that may be required. Your Electrician should realise this and advise accordingly.
 
2.5mm is not really man enough to feed a CU. rip it out and replace with 6mm or 10mm. sheds suddeny become man caves, load increases in proportion to the wife's nagging. come next winter, heaters may be required.
 
2.5mm is not really man enough to feed a CU. rip it out and replace with 6mm or 10mm. sheds suddeny become man caves, load increases in proportion to the wife's nagging. come next winter, heaters may be required.
My man cave has a 40A supply to it for just this reason!!
 
40A is a realistic load when you consider the 1000watt hi-fi, 54" flat screen tV, smart everything, couple of 2kW heaters, beer brewing equipment, motorised satellite dish, power tools when bored with TV, not tomention the hydrophonic garden.
 
40A is a realistic load when you consider the 1000watt hi-fi, 54" flat screen tV, smart everything, couple of 2kW heaters, beer brewing equipment, motorised satellite dish, power tools when bored with TV, not tomention the hydrophonic garden.
Two batches of Somerset cider, gurgling away quite happily, no more juice required...

In fact, must be almost time to bottle and sample. Or maybe sample to the bottom.
 

Reply to TT stake in outbuilding in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock