G

graham123

What size earth is acceptable for tt supply to the rod. Supply is 25mm tails from meter to Cu. 6mm earth has been installed to existing rod. Is this too small. Getting 13.1 Ze so passes by a long way. Personally i would like to see bigger earth.

Also MET has a 6mm maked up with Water bond. But when going to look at the stop cock i cannot see an earth bond their because i cannot remove the back panel from under the sink. Any suggestions on a code for this?
 
The minimum size for an earth conductor on a TT system is 2,5mm if you mechanically protect it, or 4mm if not protected. For good practice you could check it by Adiabatic equation, but 6mm is ample I would imagine.

Yes code 3 on the new EICR as long as you proved continuity, If there is continuity then reg 526.3

If you can not proved continuity then I would code it a definite 2 and perhaps even a 1, depending though on your risk assessment
 

Reply to tt supply, earth size query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

Indeed it would be. But that would mean having 2 things to disconnect instead of one. More margin for error. Of course, any diligent spark would...
Replies
6
Views
663
loz2754
L
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top