Practicing my testing and tested my first TT supply today..
It is an old farm house in the middle of no where.
I know that there is things about the install that is not upto regs.. like a BS 842 Voltage breaker for example, and the main earth needs a new copper rod and putting in a pit.
I have a few other questions about the tests i done...
1. I have been told that one of the methods for finding the resistance of earth electrode is to do a Ze test at the board, and this will also be the approx resistance of the earth electrode.. is this correct ??
2. Im not sure what i would put in for the "short circuit capacity kA" on the cert.. any ideas ??
3.I have done continuity of the ring main, I have an end to end reading of, L = 0.38, N = 0.38, and the CPC is 1.03 ????? this isnt 1.67 times greater than the liveconductors, what could cause this reading ?
4. This is a general question on any continuity test of any install.. On my assessment when im asked to do continuity of a ring final circuit will the assessor also want to see me do the L - N continuity readings and go round all sockets on the ring taking L - N readings, even though these readings are not recorded anywhere as only L - CPC (R1+R2) Will need to be recorded and shown on the test cert?
5. While testing all sockets on the ring final circuit for R1 - R2 I had a range of between 0.27 & 0.36, No spurs on the ring. Even though these reading are out of the 0.05 allowance between readings would you still class this as acceptable and write down your R1+R2 as 0.36 ?
6. There is a second CU just for storage heaters, how do you go about testing this? is this classed as a totally different inspection and will need a seperate set of test results all together?? also cant do some of the tests on this board as theres no voltage untill a certain time of the evening.
Comment on photos as you wish.. I know theres many upgrades needed.
It is an old farm house in the middle of no where.
I know that there is things about the install that is not upto regs.. like a BS 842 Voltage breaker for example, and the main earth needs a new copper rod and putting in a pit.
I have a few other questions about the tests i done...
1. I have been told that one of the methods for finding the resistance of earth electrode is to do a Ze test at the board, and this will also be the approx resistance of the earth electrode.. is this correct ??
2. Im not sure what i would put in for the "short circuit capacity kA" on the cert.. any ideas ??
3.I have done continuity of the ring main, I have an end to end reading of, L = 0.38, N = 0.38, and the CPC is 1.03 ????? this isnt 1.67 times greater than the liveconductors, what could cause this reading ?
4. This is a general question on any continuity test of any install.. On my assessment when im asked to do continuity of a ring final circuit will the assessor also want to see me do the L - N continuity readings and go round all sockets on the ring taking L - N readings, even though these readings are not recorded anywhere as only L - CPC (R1+R2) Will need to be recorded and shown on the test cert?
5. While testing all sockets on the ring final circuit for R1 - R2 I had a range of between 0.27 & 0.36, No spurs on the ring. Even though these reading are out of the 0.05 allowance between readings would you still class this as acceptable and write down your R1+R2 as 0.36 ?
6. There is a second CU just for storage heaters, how do you go about testing this? is this classed as a totally different inspection and will need a seperate set of test results all together?? also cant do some of the tests on this board as theres no voltage untill a certain time of the evening.
Comment on photos as you wish.. I know theres many upgrades needed.