Im sorry but,
I prefer to inform what the requirements are rather than any personal options which may convey stricter results than are needed and may confuse.....

Totally agree there Des.

Didnt mean to preach!:D

However, generally its not hard to get a result below 100, without even trying!
 
Last edited by a moderator:
That 21 ohms is the suppliers maximum or stated, for the star point of the supply transformer and their own earth electrode
The maximum for the operation of a 30m/amp rcd is 1667 ohms however,

Any reading of your earth (which includes the suppliers 21ohms)should be under 200ohms

Anything above this figure could be considered as unstable,because for instance it may rise in drier whether when soil conditions are different

The 100ohms mentioned is an NIC figure erring on the side of extra safety and is guidance for their members only,the IEE regulations are the figures to follow for everyone else

Excellent des, Thanks for a good answer. Just what i wanted to know

It is difficult to see from your pics but the lower cu has a link from its earth terminal to the one above. My guess from what you say is that the yellow/green from the lower goes to an earth rod as well as another one from the the upper cu to a different earth rod. In this case surely they are effectively the same assembly, possibly a second rod being put in to improve the first. That being the case the only concern as I see it is that one rod is a rods length away from the other.


This is exactly what has happened here.. Just as you've said.

So as you say this second rod would have been put in to improve the Ze/electrode reading?

Do i just take the lowest reading from either rod and record this on both of the sepearte test results for each CU?
 
Last edited by a moderator:

Reply to TT Supply, Testing Questions.. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
250
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
723
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
695

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
325
Interesting question & always gonna get different views on this. EICR testing seems to have changed over the years & not by us the Electricians...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top