Would appreciate some advice please.
I'm wiring a TT system and am un-sure of what earthing is required.
Reg 411.3 - 'Requiremnts for fault protection', says that protective equipotential bonding is required to extraneous-conductive-parts which i'd already done. Am i correct in saying that there is no requirement for cross bonding in the bathroom and kitchen now?
Also could someone clarify how Automatic dis-connection of supply is achieved?
My understanding of the reg's are that if the Zs value is too high, (which is most likely for all TT systems) to use tables 41.2 to 41.4 for overcurrent devices, then it's acceptable to rely soley on the operation of the RCD to trip within .2s at 2xI delta n or greater (Note 2 below Table 41.1)
Reg 411.5.2 says that either an RCD or overcurrent device may be used, pref' the RCD with overcurrent devices on circuits.
So as my Zs value is way too high to use overcurrent devices for ADS then its's fine to rely on the RCD for ADS within the required time....?
Thanks in advance
I'm wiring a TT system and am un-sure of what earthing is required.
Reg 411.3 - 'Requiremnts for fault protection', says that protective equipotential bonding is required to extraneous-conductive-parts which i'd already done. Am i correct in saying that there is no requirement for cross bonding in the bathroom and kitchen now?
Also could someone clarify how Automatic dis-connection of supply is achieved?
My understanding of the reg's are that if the Zs value is too high, (which is most likely for all TT systems) to use tables 41.2 to 41.4 for overcurrent devices, then it's acceptable to rely soley on the operation of the RCD to trip within .2s at 2xI delta n or greater (Note 2 below Table 41.1)
Reg 411.5.2 says that either an RCD or overcurrent device may be used, pref' the RCD with overcurrent devices on circuits.
So as my Zs value is way too high to use overcurrent devices for ADS then its's fine to rely on the RCD for ADS within the required time....?
Thanks in advance