ChrisElectrical88

-
Mentor
Nearly Esteemed
Arms
Joined
Feb 23, 2013
Messages
2,094
Reaction score
1,681
Location
Wales
Hi, I have a lad working on a farm at the moment and he phoned me today panicking at a high ZE and PSC. 3.50ohms and 79kA. I asked him what system was in place and he said TN-S. I then told him to go earth rod hunting. Got a phone call back saying he couldn't find anything. I'm on a course this week so I don't have access to my regs etc. Are these good TT reading? (I'm not to familiar with TT so don't have much clue without my books) and should I tell him to open his eyes and go searching again? Or should I tell him to leave our new circuit switched off and go and investigate myself?

Sorry if its a stupid question.
cheers
 
that's better. however, that Ze is not acceptable so get DNO to sort it out. meanwhile leave any of your new work disconnected from supply.
 
Those results are good and consistent for a TT install but obviously way out for a TNS.
If he thinks it is a TNS ()and has seen the connection on the cable) then I would say that the earth connection at the cable is not good and the eareth is being provided by a service pipe through the bonding.
DNO call out to repair.
However do check again it is not TT because it can be a bit embarrassing if it is!
 

Reply to TT system help. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
707
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top